how to calculate the neautral earthing conductor size for a
500kva dg set.
Answers were Sorted based on User's Feedback
Answer / krl raju
If alternator voltage is considered 415 V, then rated
current of the Alternator is
=500*1000/(1.732*415)=695.6Amps.
Hence we need to select the neutral conductor to withstand
the half of the full load current i.e 350Amps
| Is This Answer Correct ? | 9 Yes | 2 No |
Answer / sakthivel
hi mr krl raju sir i want which size of contuctor you
chuse about 350 amp neutral earth comtuctor give full
details
| Is This Answer Correct ? | 2 Yes | 0 No |
how do we select a copper power cable for a 10 HP, 1440 rpm, 440V, 3 phase AC motor?
Why scr and igbt used in ups systeam ????
why do you want leave the company
wat is the first thing dat is needed, 2 lay a cable in some area??
Can you any explain about active,reactive and apparent power in power system with example.
WHAT IS DIFFERENCEN BETWEEN CURRENT AND VOLTAGE?
Explain how you intend to work under pressure to meet up with deadline target?
How conventional fire alarm system works?
Why we Do not connect the windings of the motor in delta? & what would happen if we do that? I mean the winding themselves not the three lines that are coming to the motor?
What is pi controller?
The advantages of Magnetic flux leakage technique over Ultrasonic technique for non distructive testing of material.
what is difference between earth and ground?/
3 Answers Sree Rayalseema Green Energy Limited SRGEL,
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)