FOR WHICH FAULTS OR CONDITIONS DOES A TRANSFORMER
DIFFERENTIAL PROTECTION DOES NOT OPERATE???
Answers were Sorted based on User's Feedback
Answer / thiru
transformer differential protection does not operate when
there is out zone fault.because that time two sides of CT's
sense same current. there is no difference of current.so
the relay does not operate.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / v.selvakumar
through fault or external fault it won't operate.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / zahid ali
Turn to turn fault it won't operate.
in other case if the neutral is grounded grounded through
high impedance or Resisted earth fault it wouldn't be
operate on ground fault.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / zahid ali
because there is no difference in the current at the ends
of a winding with shorted turn: a turn fault would have to
burn through major insulation to ground or another phase
before it could be detected
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / minu
not the ground fault, if its settings are kept low enough,
it will operate for ground fault also. i am looking for
some other answer.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / siddharth tayade
onely internal fault is detected by the diffrential relay
it will not trip under through fault condition
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / minu
no. i am asking abt the in-zone faults only. for what in-
zone faults or some conditions will it not operate.
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / minu
hi zahid, thanks for the reply. can u pl elaborate a bit on
why it wont operate on turn to turn faults or for other
cases that u mentioned.
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / minu
does that mean that a shorted turn fualt wont be detected
by any other relay too???
| Is This Answer Correct ? | 1 Yes | 2 No |
How to calculate meter constant in HT yard pls give me example for this issue
1 Answers Juniper Networks, MacLellan,
Why have the transformer one earthing to their neutral? Why have the transformer many earthing to their body?
how are reversing the direction of rotation of dc motor
What is the criteria in selecting Air circuit breaker(ACB) & Moulded case circuit breaker(MCCB) for a particular range?
why the single phse machine can not run by the three phase supply.
what is the function of Droop CT and where it is used?
Why negative feedback is preferred in the control system?
Safety devices in SF6 Circuit Breaker?
what is real time system type definition
How the FM200 Gas Supression System wil Work????
What is difference between PLC and SCADA
13 Answers Uflex, Vimal Fire Controls,
Why the Transformer connection is changing in different transformer?(Like Star & Delta,Delta & Delta,Star & Star,Delta Star) From that connection where it is used?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)