FOR WHICH FAULTS OR CONDITIONS DOES A TRANSFORMER
DIFFERENTIAL PROTECTION DOES NOT OPERATE???
Answers were Sorted based on User's Feedback
Answer / thiru
transformer differential protection does not operate when
there is out zone fault.because that time two sides of CT's
sense same current. there is no difference of current.so
the relay does not operate.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / v.selvakumar
through fault or external fault it won't operate.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / zahid ali
Turn to turn fault it won't operate.
in other case if the neutral is grounded grounded through
high impedance or Resisted earth fault it wouldn't be
operate on ground fault.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / zahid ali
because there is no difference in the current at the ends
of a winding with shorted turn: a turn fault would have to
burn through major insulation to ground or another phase
before it could be detected
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / minu
not the ground fault, if its settings are kept low enough,
it will operate for ground fault also. i am looking for
some other answer.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / siddharth tayade
onely internal fault is detected by the diffrential relay
it will not trip under through fault condition
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / minu
no. i am asking abt the in-zone faults only. for what in-
zone faults or some conditions will it not operate.
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / minu
hi zahid, thanks for the reply. can u pl elaborate a bit on
why it wont operate on turn to turn faults or for other
cases that u mentioned.
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / minu
does that mean that a shorted turn fualt wont be detected
by any other relay too???
| Is This Answer Correct ? | 1 Yes | 2 No |
What is difference b/w Microwave and OPGW ??
can volts/Hz be relied upon to use 460v,60Hz electric motors on a 380v,50Hz power supply?
plese send me the oces/dgfs sylabus and previous year question pattern of electrical engg.?
Can anybody tell me what the breakdown voltage is for air and what it is for transformer oil please?
We have 110Vac ,10A ac supply which is converted into 110VDC & How much DC current? which factor is reqired for dc current calulation?
What is the difference between security constraint unit commitment and security constraint optimal power flow?
0 Answers College School Exams Tests,
How to check it good or bad capacitor
why it is important to earth neutral of 3 phase transformer?
9 Answers IBM, ITC Indian Tobacco Company, RRB, UDS,
What are the condition for parallel operation of transformers?
How does a clampmeter measures dc current
Difference between RCCB, RCBO and ELMCB.
an off load but energized 11/0.4 KV, 1250 KVA T/F has a power factor of 0.65(capacitive)..!! why is it so, though T/F being an inductive device ??
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)