Answer / ram niveth
REF is a backup protection for transformer incipient
faults.
if differential fails REF comes on line.
if both protections are used , usually REF time setting
will be less than differential setting
| Is This Answer Correct ? | 15 Yes | 27 No |
Answer / shipra
restricted earth faukt protn is for unprotected zone of
neutral to earth.
Diffetential protn will work only if the falt is with in
zone of CT so that it can get a differential current. If
there is a fault between neutral CT and earth the fault
will be feeded and no diffential current will be there as
it is balaced through primary side, secndary side & nutral.
| Is This Answer Correct ? | 19 Yes | 32 No |
Answer / erharisheee51
RESTRICTED EARTH FAULT PROTECTION IS GENERALLY PROTECT FROM
THE DEFFERENTIAL CURRENT WITH IN THE GENERATOR CORE , WHERE
AS DIFFERENTIAL PROTECTION IS USED FOR OVERALL DIFFERENTIAL
| Is This Answer Correct ? | 5 Yes | 23 No |
Answer / pradeep
mainly there is some drawbacks in differential protection.
the protection is mostly surrounding at the certain region.
for example, if the transmission line length is 10km
means,we locate differential protection in between the
transmission line we can't able to protect the outerside of
the transmission line. so that we go for earth fault
protection. earth consist the infinite resistance.
| Is This Answer Correct ? | 4 Yes | 32 No |
what is meant by magnetic flow meter ? explain its working principle ?
where can i get vijaya electricals limited in hyderabad interview auestions can u give me the website address plz
What is the Ramping rate of Generator. What mena Ramping rate
How to calculate the electrical load for a standard telecom BTS shelter and choose the DG set capacity for the same load?
What happen if we have run 415 V,50Hz designed motor at on 480V,60HZ
why transformer comes only in standard rating like 11kv,33kv,66kv....and not like 33.33kv and so on?
Why r used of cable 50sq.mm and above size cable in 3.5 core. And below size in 4 core ? any technical reason please explain it
what is meant by k-rating in isolation transformer?what is k9, k14 stands for?
which relay is better , instantaneous or IDMT relay .
A 11KV, 1200 A breaker combination fixed in a cubicle for HT motor.Is normally for 11 KV motor fuse is using? if Yes, What range fuse is required?
What can a fresh(without experience) electrical engineer contribute to NTPC( Or any PSU company) growth?
if u have to run a 300kw moter then what is ur choice HT or LT switchgear & explain why?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)