WHY IS THE EARTH FAULT CURRENT ALWAYS LESS THAN THE NORMAL
CURRENT??
Answers were Sorted based on User's Feedback
Answer / rvg.msceb
earth fault current will be less because the voltage
difference between line and ground is V/1.732 and that of
line to line is V. since the voltage is less, the earth
leakage current will be 57.7% of line to line faults.
| Is This Answer Correct ? | 52 Yes | 7 No |
Answer / v.selvakumar
we can't say that the fault current lessthan the normal
current ,fault current depend upon the system parameters
i.e resistance ,inductance
| Is This Answer Correct ? | 20 Yes | 17 No |
Answer / devit patel
please mention the equipment under consider,because earth
falut current directly depens on zero sequance impendance
| Is This Answer Correct ? | 5 Yes | 3 No |
Answer / abhishek badh...
Earth fault current is depand upon zero sequence impedence.
impedence is more than e f c is less compared to line
current.
| Is This Answer Correct ? | 3 Yes | 3 No |
Answer / minu
thanks for the reply, but i meant to ask that why is the
earth fault current lesser than other type of fault
currents.
| Is This Answer Correct ? | 7 Yes | 10 No |
Answer / vibol seng
I have agreed with answer No 4 any way in distribution
system we have met a lot time (80%) prepaire phase to phase
short circuit.
| Is This Answer Correct ? | 0 Yes | 3 No |
Answer / gaurav
earth falt current current is nothing but the leakage
current and leakage current is alwase less than line or
neutral current.therefore earth fault current is always
less than normal current.
there should not be the common conductor for the earth and
neutral for the safety and to minimizing the ground
potential differances.
| Is This Answer Correct ? | 2 Yes | 16 No |
WTA used cb?
What is meant by Energy Efficient Transformers??? give significance
How earthing of switchgear system to be done.
why we are used D.c. voltage in L.T.side or controling side.we can use UPS also ,in place d.c. voltage
can we use 3 phase UPS for Motors and Other Machines
Dear sir/mam Iwant complete details of Naintenence of 33kv/433v Transformer having 1250 KVa
I have two AC generators, the first rated 2680KVA for 380V/4345A/pf:0.7 and the second rated 3461KVA for 5500V/363A/pf:0.8. I want to parallel the two generator to a bus. The second generator passes through a transformer to down the voltage to 380V and a part of its power goes to another bus so that it's only a part of the total power of the second generator taht goes to the considered bus. I have two Basler DECS100 AVR regulator. How can I make the synchronization ? What others equipments must have ?
a bulb of 100W and anather bulb of 200W , rated supply voltage 230v.when supply voltage is reduced to 100v,which bulb will give more light? and why with calculation?
how to calculate current and voltage in a same circuit?
how a single machine can act as both motor and generator? and give explanation interms of connections?
What happens if we give the supply to the rotor of induction motor and make its terminal shorted?
What is pd controller?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)