In domestic supply, when neutral touches earth the earth
leakage trips. Does this mean that if the star (neutral)
point of an alternator is earthed that power will flow to
earth i.e. a direct short to earth?
NO. Normally for distribution purposes the utilities are
using Dy transformers. Hence the zero sequence current
produced by the consumer side fault is not transfered to
the High voltage side.
The earth fault current in the LT side is circulated from
the fault point to the Dy transformer neutral and the
faulted phase.
| Is This Answer Correct ? | 2 Yes | 0 No |
whats relation b/w motor current & friqency
WHAT IS DIFFERENCE BETWEEN CAPACITOR AND CAPACITANCE?
When neutral is grounded in electrical circuit?
where we use the SFU & FSU?
what is difference between VAT & CST
which is the slowest motor? and wt is speed ?
How to get a multiplier in 11kv energy meter?
y we are used signal conditioner in capacitive transducer
What is metering cubical? What is the use?
I Need standard operation procedure(SOP)for 500kva Oil type transformer oil filtration & Procedure for IR value checking.
how is capacitor bank look like
advantage of cu cable over al cable
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)