In domestic supply, when neutral touches earth the earth
leakage trips. Does this mean that if the star (neutral)
point of an alternator is earthed that power will flow to
earth i.e. a direct short to earth?
NO. Normally for distribution purposes the utilities are
using Dy transformers. Hence the zero sequence current
produced by the consumer side fault is not transfered to
the High voltage side.
The earth fault current in the LT side is circulated from
the fault point to the Dy transformer neutral and the
faulted phase.
| Is This Answer Correct ? | 2 Yes | 0 No |
Comparative difference between 33Kv & 66KV for transmitting the load of 7 MW at a distance of 34 Km.
What is the min and max ohmic value for earthing?
What is nyquist contour?
for high freq ac,why we first convert AC to DC and then DC to high freq.AC
how to detect the presence of underground cable(while digging road)etc. -give the name of instrument
explain which quantities change in the starting and the and the running condition in induction motor
who is ohm's and his law ?
In a 132KV Grid Station where voltage level is 132KV, here, why the rating of Surge arrests installed 120KV ?
what is the difference between the electrical and electroncis
WHY HUMMING SOUND OCCURED IN HT TRANSMMISSION LINES ?
Explain the purpose of inductor in an electric circuit?
What is resonant peak?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)