How to take Transformer oil Break down voltage test?
Answers were Sorted based on User's Feedback
Answer / dinesh kumar
TRANSFORMER OIL BDV is carried out as per IS-336 for nomal
and IS-12463 for High viscosity oil.
1.Take one sample from top of Transformer and one from the
bottom of transformer.
2.The BDV of oil should withstood min 50 KV
3.The gap between the test sample is 2.5mm maintained
4.Each sample(top/bottom) should be checked seperately
5.Procedure
a.Voltage should be gradually increased from 0.
b. At one point Flash will take place and that point is
termed as Bread down Voltage
Is This Answer Correct ? | 119 Yes | 10 No |
Answer / sri rama murthy
the breakdown voltage need not be 50kv but the min BDV is
30kv at 2.5mm gap between the electrodes
Is This Answer Correct ? | 26 Yes | 3 No |
Answer / hamed
Regarding the withstand voltage I think It depends on the
type and quality of the oil itself.
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / deepak sharma
Please anyone can tell me the dia. of the electrodes?????
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / v.b.vijay anand
At first thing you maintain the electrical norms..To Take one sample from top of Transformer and one from the
bottom of transformer.
On before take oil samples you should confirm the moisture particles removed are not..
And then removed the air boubles in that vessel between the electrode...
The BDV of oil should withstood min 50 KV...
The gap between the test sample is 2.5mm maintained..
Voltage should be gradually increased from 0.
You will wait min 30min then only you will get good result..
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / muhammad owais
tell me why take sample both side (top/bottom)?
why not take from bottom any problem
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / saravanan.m
*Take one sample from top of Transformer and one from the
bottom of transformer.
*The BDV of oil should withstood min 50 KV
*The gap between the test sample is 2.5mm maintained
*Each sample(top/bottom) should be checked seperately
*Procedure
a.Voltage should be gradually increased from 0.
b.At one point Flash will take place and that point is
termed as Bread down Voltage.
*If its withstand means the viscosity of transformer oil is
good
Is This Answer Correct ? | 4 Yes | 7 No |
Answer / suthagar.s
that means the transformer oil withstand the temparature
capacity that is called as breakdown voltage test in
transformer
Is This Answer Correct ? | 6 Yes | 45 No |
Which starter can be used for 3 phase verriable speed (2 stator wdg) induction motor ?
What is harmonics in AC waves. How it is generated? How it will effect the system network? how can eliminate it?
what is encoder & its use?
Why Magnetic Core Balance test is performed only on Star side of Transformer and not on Delta Side of Transformer (Vector Group Dyn11)?
why 6.6,11,22,33,66kv? what basis they have considered?
what happen if drive input fail momentry at 48.5 HZ frequency?
What is it mean Transformer 100/133MVA Power Transformer, significance of 100/133 MVA and 230/115KV please
On what basis primary and secondary of a transformer is chosen?
How will you calculate the correct KWH value if your CT is 600/5 and your KWH meter is rated for 100/5
If carbon brushes spring tension either loose or tight, what happen on Motor performance During Full load Operation?
Types of 132KV and 222 KV protection.
Wat is da difference b/w neutral earthing and unearthed system?