Answer / dinesh kumar
TRANSFORMER OIL BDV is carried out as per IS-336 for nomal
and IS-12463 for High viscosity oil.
1.Take one sample from top of Transformer and one from the
bottom of transformer.
2.The BDV of oil should withstood min 50 KV
3.The gap between the test sample is 2.5mm maintained
4.Each sample(top/bottom) should be checked seperately
5.Procedure
a.Voltage should be gradually increased from 0.
b. At one point Flash will take place and that point is
termed as Bread down Voltage
| Is This Answer Correct ? | 119 Yes | 10 No |
Answer / sri rama murthy
the breakdown voltage need not be 50kv but the min BDV is
30kv at 2.5mm gap between the electrodes
| Is This Answer Correct ? | 26 Yes | 3 No |
Answer / hamed
Regarding the withstand voltage I think It depends on the
type and quality of the oil itself.
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / deepak sharma
Please anyone can tell me the dia. of the electrodes?????
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / v.b.vijay anand
At first thing you maintain the electrical norms..To Take one sample from top of Transformer and one from the
bottom of transformer.
On before take oil samples you should confirm the moisture particles removed are not..
And then removed the air boubles in that vessel between the electrode...
The BDV of oil should withstood min 50 KV...
The gap between the test sample is 2.5mm maintained..
Voltage should be gradually increased from 0.
You will wait min 30min then only you will get good result..
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / muhammad owais
tell me why take sample both side (top/bottom)?
why not take from bottom any problem
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / saravanan.m
*Take one sample from top of Transformer and one from the
bottom of transformer.
*The BDV of oil should withstood min 50 KV
*The gap between the test sample is 2.5mm maintained
*Each sample(top/bottom) should be checked seperately
*Procedure
a.Voltage should be gradually increased from 0.
b.At one point Flash will take place and that point is
termed as Bread down Voltage.
*If its withstand means the viscosity of transformer oil is
good
| Is This Answer Correct ? | 4 Yes | 7 No |
Answer / suthagar.s
that means the transformer oil withstand the temparature
capacity that is called as breakdown voltage test in
transformer
| Is This Answer Correct ? | 6 Yes | 45 No |
A dc motor running on dc drive whose input is 3ph AC what will happen if we change the phase sequence of dc drive for e.g (R Y B) is connect as R B Y, will the motor run as same as previously running before changing phase without any effect
what are the disadvantages in GIS over AIS
What is the difference b/w earthing & grounding?
Why the transformers are rated in KVA ? in new view
what is the workimg of ct &pt?
What is the si unit
WHY MOSTLY BATTERY VOLTAGE IS IN MULIPLE OF 2 LIKE 2V,4V,8V,16V,18V....
what is the work of trip circuit supervision relay?
What is the maximum No. of out going mccbs permitted from an LV distribution paqnel? What is the ampere relation between incomer and out going switch gears/mccbs?
What is switching over voltage?
Why material of brush is carbon in motors why not other material.
what is single phase motor?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)