How to take Transformer oil Break down voltage test?
Answers were Sorted based on User's Feedback
Answer / dinesh kumar
TRANSFORMER OIL BDV is carried out as per IS-336 for nomal
and IS-12463 for High viscosity oil.
1.Take one sample from top of Transformer and one from the
bottom of transformer.
2.The BDV of oil should withstood min 50 KV
3.The gap between the test sample is 2.5mm maintained
4.Each sample(top/bottom) should be checked seperately
5.Procedure
a.Voltage should be gradually increased from 0.
b. At one point Flash will take place and that point is
termed as Bread down Voltage
| Is This Answer Correct ? | 119 Yes | 10 No |
Answer / sri rama murthy
the breakdown voltage need not be 50kv but the min BDV is
30kv at 2.5mm gap between the electrodes
| Is This Answer Correct ? | 26 Yes | 3 No |
Answer / hamed
Regarding the withstand voltage I think It depends on the
type and quality of the oil itself.
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / deepak sharma
Please anyone can tell me the dia. of the electrodes?????
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / v.b.vijay anand
At first thing you maintain the electrical norms..To Take one sample from top of Transformer and one from the
bottom of transformer.
On before take oil samples you should confirm the moisture particles removed are not..
And then removed the air boubles in that vessel between the electrode...
The BDV of oil should withstood min 50 KV...
The gap between the test sample is 2.5mm maintained..
Voltage should be gradually increased from 0.
You will wait min 30min then only you will get good result..
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / muhammad owais
tell me why take sample both side (top/bottom)?
why not take from bottom any problem
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / saravanan.m
*Take one sample from top of Transformer and one from the
bottom of transformer.
*The BDV of oil should withstood min 50 KV
*The gap between the test sample is 2.5mm maintained
*Each sample(top/bottom) should be checked seperately
*Procedure
a.Voltage should be gradually increased from 0.
b.At one point Flash will take place and that point is
termed as Bread down Voltage.
*If its withstand means the viscosity of transformer oil is
good
| Is This Answer Correct ? | 4 Yes | 7 No |
Answer / suthagar.s
that means the transformer oil withstand the temparature
capacity that is called as breakdown voltage test in
transformer
| Is This Answer Correct ? | 6 Yes | 45 No |
what is the circulate the diesel in DG in side pls tell parts name and picture with circulate the diesel
when a three phase motor in running condition consumes 2A in each phase,and if one of the phase gets fails what will be the consumption in other two phases
All the voltage drops and the source voltage added together in a series circuit is equal to
there is a power transformer 66/11kV in delta-delta connection has 5 feeder coming out from the secondary side. One of the feeder in it normally loaded (loaded than other feeder)and this feeder usually trips with double OCR causing the bank transformer to trip. Now if the load of this feeder is put on other transformer then that no problems occurs on that transformer or the load. However normally all the test(IR, PI, short ckt, open ckt,grounding test and other ) has been conducted for this but evertything transformer..... I am not geting what is the actual problem...
in control scheme dc logic wiring commonly using negative loop,what is the reason?if we use positive looping what will happen?
please design a rectifier with batteries for below requirement and also explain how you calculate this solution, Load = 700Amp DC Backup time = 6 hour. please explain briefly ?????
CAN CU XLPE/PVC CABLE BE USED INPLACE OF LOW NOISE SCREENED CABLE? KINDLY GIVE REASONS
why transformer tank is in rectangular shape what happen when it is in step shape
how to calculate the bus bar current rating
whether choke act as a voltage regulator in tubelight or not?
What is the permissible maximum flux density in transformer core?
How can i calculate heat load ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)