how to caluculate APFC panel rating, my running Load is
1320KW, Present P.F 0.76 to 0.8 we need 0.98 p.f
Answers were Sorted based on User's Feedback
Answer / maprayil
KVAr is square root of (KVA2-kW2). In your case the system KVAr at P.F. 0.76 lag is 1129 KVAr; and P.F. 0.80, it is 990 KVAr. (These are the KVAr values required to take your system P.F. to Unity or 1.00). Please note the following values:-
With a running load of 1320 kW, the Maximum Demand (KVA) of your system at 0.76 PF is 1737 KVA; and at P.F. 0.80, it is 1650 KVA. At a P.F. of 0.98, the Max Demand would be 1347 KVA (KVA = kW/P.F.).
Now that you have the system KVAR & KVA values, the simplest way is to calculate the system KVAR after P.F. is improved to 0.98 lag (your desired value). This can be worked by (considering initial P.F. 0.76):-
KVAR = Square root ((KVA+kW)*(KVA-kW))
= Square root ((1347+1320)*(1347-1320)
= Square root (2667 * 27) = SQRT 72009
= 268 KVAr.
So KVAR required for improving the P.F. of 1320 kW running load from 0.76 to 0.98 is 1129 KVAR (initial system KVAR) minus 268 KVAr (final system KVAR), i.e., 861 KVAr. This KVAR needs to be installed in multiple steps with automatic switching arrangement.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / manish mangla
Actually it is very simple.You know the present pf and
desired pf too.so you can use the formula:
Kvar=kwh(tan(inverse)phi1-tan(inverse)phi2)
Phi1=actual or present pf
Phi2=desired pf
Is This Answer Correct ? | 1 Yes | 1 No |
Answer / s. k. mishra
KVAR^2 = KVA^2 - KW^2 = KVA^2 - KVA^2 * pf^2= KVA^2(1-pf^2)
THEREFORE KVAR= KVA [(1-pf^2)]^1/2
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / tajinder singh
kw=1320
present PF = 0.76
kva =1320/0.76
=1737
for unity pf u require capacitors Panel =1129 kVAr
for 0.98 pf u require capacitors panel =858 kVAr
Is This Answer Correct ? | 2 Yes | 4 No |
Answer / vijay
Kvar=KVA(1-P.F)
KVA=KW/P.F
Kvar=Kw(1-P.F)/P.F
=1320(1-0.98)/0.98
=250
Is This Answer Correct ? | 20 Yes | 33 No |
Answer / cibi
by using delsigma relations or fiuys charts apf panel rating
could be determined
Is This Answer Correct ? | 18 Yes | 36 No |
DIFFERENCE BETWEEN CODES,STANDARDS & SPECIFIFCATIONS?
what is the thermodynamics?
Hello sir! I hav read the above discussions about PSU.I hav 72% aggregate in Mechanical bt i do had a back in 1 subject,so m i too eligible for PSU?
what is the difference between the air preheater & air blower?
What is means turbine
From a group of 7 men and 6 women, five persons are to be selected to form a committee so that at least 3 men are there on the committee. In how many ways can it be done? A. 564 B. 645 C. 735 D. 756 E. None of these
what is the difference between dross and scale?
what is the difference between 1st angle and 3rd angle projection?
what is the Reynolds number
give the function of thermostat
What is the cause of cylindrical liner overheating?
what is pulverisation