Answer / kannan.sj
first u should know
1,The connected load of transformer or load factor
2,Highest connected load / motor in the transformer and its
starting type
3, diversity factor
because
KVA demand at 0.8 p.f =connected load x LF x DF
-------------
efficiency X p.f
starting current of highest KW load takes 6 times of full
load current. so we to check it whether the transformer has
the capability to feed the load or not during starting. its
the important thing while considering trafo selection..
| Is This Answer Correct ? | 57 Yes | 6 No |
Answer / guest
You need to know the load type and calcuation of schort
circuit
| Is This Answer Correct ? | 25 Yes | 14 No |
Answer / ahfaz
1] we have to know the KVA load required
2] we have to know the percentage of impedance in the winding
3] Indoor or Outdoor
4] Type of cooling
5] Maximum temperature required
Thanks & regards
Ahfaz
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / shaista
SECONDARY LOAD VOLTAGE
KVA Rating
application of use
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / mohammed hussain a
Load Current,Load Voltage and Load Power factor(Secondary
Side). It may 3 Phase or 1Phase.
For 3phase Power in KVA = 1.732*V*I/0.8*1000
For 1 Phase in KVA = V*I/1000.
The rating of the transformer can be identified from the
above formula.
| Is This Answer Correct ? | 13 Yes | 11 No |
Answer / mgm
calculate all connected load like lighting load power load
motors ahu etc, calculate the 3 phase current and multiply
it with 1.25%
we will get the transformer size
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / manasa
First we have to know about the load consumption, then
diversity factor that is demand in KW and then in KVA
| Is This Answer Correct ? | 7 Yes | 10 No |
defination of static variable compensator
What is the Ramping rate of Generator. What mena Ramping rate
while calculating demand in my company the present load in kw is 212.... there 125kvar capacitor bank is installed by spliting as 50 in departments...the diasplay in panek biard shows 175kw... how could we know the amount of kvar used to compensate the kva
How to select power cable for machine
can we use transformer for 70 Hz?
what is effect of leading power facter on the system and billing
what is meant by negative sequencing in power system.explain in detail
Why do we give DC excitation to AC Synchronous motor??
9 Answers Lance, MBM, Polycab,
how to find out 3 phase complex power in per unit in unbalanced system?
A 230V dc shunt wound motor has an armature resistance of 0,15Ω.When operating on no load at 650 rev/min the armature current is 6A . The motor takes a full load current of 85A. Calculate the full load speed if the field flux is (i) maintained constant (ii)reduced by 0,03
what is work of CTPT in 33/11kv Substation
What is the real use of reactive power in a electrical system other than loss (inductive &capacitive).I want to know its real physical significance.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)