WHAT ARE THE FACTORS REQUIRED FOR SELECTION OF TRANSFORMER
RATING?
Answers were Sorted based on User's Feedback
Answer / kannan.sj
first u should know
1,The connected load of transformer or load factor
2,Highest connected load / motor in the transformer and its
starting type
3, diversity factor
because
KVA demand at 0.8 p.f =connected load x LF x DF
-------------
efficiency X p.f
starting current of highest KW load takes 6 times of full
load current. so we to check it whether the transformer has
the capability to feed the load or not during starting. its
the important thing while considering trafo selection..
Is This Answer Correct ? | 57 Yes | 6 No |
Answer / guest
You need to know the load type and calcuation of schort
circuit
Is This Answer Correct ? | 25 Yes | 14 No |
Answer / ahfaz
1] we have to know the KVA load required
2] we have to know the percentage of impedance in the winding
3] Indoor or Outdoor
4] Type of cooling
5] Maximum temperature required
Thanks & regards
Ahfaz
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / shaista
SECONDARY LOAD VOLTAGE
KVA Rating
application of use
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / mohammed hussain a
Load Current,Load Voltage and Load Power factor(Secondary
Side). It may 3 Phase or 1Phase.
For 3phase Power in KVA = 1.732*V*I/0.8*1000
For 1 Phase in KVA = V*I/1000.
The rating of the transformer can be identified from the
above formula.
Is This Answer Correct ? | 13 Yes | 11 No |
Answer / mgm
calculate all connected load like lighting load power load
motors ahu etc, calculate the 3 phase current and multiply
it with 1.25%
we will get the transformer size
Is This Answer Correct ? | 1 Yes | 1 No |
Answer / manasa
First we have to know about the load consumption, then
diversity factor that is demand in KW and then in KVA
Is This Answer Correct ? | 7 Yes | 10 No |
what is the difference between relay, contactor
4 Answers BRSS, Vishay Intertechnology,
why we need the starters for motors
i have completed deee and i've (June2012-feb 2015 experience in electrical maintenance in pvt ltd company.company having HT & LT electrical power.how to apply electrical C-license ,NOW I was resigned my job,what are requirements of applying for c-license
How much kv gas generator is needed to run 2 hp and 1 hp airconditioners, plus a refrigerator and 4 Tvs
why+ve is earthed in electrostatic precipitator in thermal power plant
which one is rotating transformer-single phase induction motor or 3 phase squirrel cage motor?
why the India electrical supply transmission loss is high when compare to us
If single phase supply is 220v. then why three phase supply is 660?
In zero voltage we can pass supply to our body means we cant get shock its true ? how we can do it ?
why is the transmission voltage is multiple of 11?
what is %impedanece
How dc generators direction can be reversed ??
2 Answers GPSC Gujarat Public Service Commission,