WHAT ARE THE FACTORS REQUIRED FOR SELECTION OF TRANSFORMER
RATING?
Answers were Sorted based on User's Feedback
Answer / kannan.sj
first u should know
1,The connected load of transformer or load factor
2,Highest connected load / motor in the transformer and its
starting type
3, diversity factor
because
KVA demand at 0.8 p.f =connected load x LF x DF
-------------
efficiency X p.f
starting current of highest KW load takes 6 times of full
load current. so we to check it whether the transformer has
the capability to feed the load or not during starting. its
the important thing while considering trafo selection..
| Is This Answer Correct ? | 57 Yes | 6 No |
Answer / guest
You need to know the load type and calcuation of schort
circuit
| Is This Answer Correct ? | 25 Yes | 14 No |
Answer / ahfaz
1] we have to know the KVA load required
2] we have to know the percentage of impedance in the winding
3] Indoor or Outdoor
4] Type of cooling
5] Maximum temperature required
Thanks & regards
Ahfaz
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / shaista
SECONDARY LOAD VOLTAGE
KVA Rating
application of use
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / mohammed hussain a
Load Current,Load Voltage and Load Power factor(Secondary
Side). It may 3 Phase or 1Phase.
For 3phase Power in KVA = 1.732*V*I/0.8*1000
For 1 Phase in KVA = V*I/1000.
The rating of the transformer can be identified from the
above formula.
| Is This Answer Correct ? | 13 Yes | 11 No |
Answer / mgm
calculate all connected load like lighting load power load
motors ahu etc, calculate the 3 phase current and multiply
it with 1.25%
we will get the transformer size
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / manasa
First we have to know about the load consumption, then
diversity factor that is demand in KW and then in KVA
| Is This Answer Correct ? | 7 Yes | 10 No |
why is control bus bi-directional?
why do we need a 4th wire in 3phase 3wire transmission line
Application Comparison between 22KV (UE)and 33KV (E) system. Are we allowed to use 33KV (E) cable in lieu of 22KV (UE) cable. What are the technical disadvantages.
(1)Can earth and be conected together (2) what is the diferent between earth & neutral
What are the applications of different multistage amplifiers?Plz also write advantages of these amplifiers? Thaaaaaaaaanx
please send me previous year questions of jspl through which i could prepare myself for the test.
Why HT cable have only 3 core ?
What is the maximum and minimum rating of UPS?
what is the difference between inductive load and capacitive load?give me some examples in general
Control cables in S's will carry 1000v which is AC R DC? Pls answer me
What is the formula for calculating impedance of transformers connected parallel at fault level 50KA?
How will you calaculate the Ct ratio based on connected load 500KVA,and 11KV supply ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)