What accessories required to give the motor with given
circuits and do you know the ratings of those accessories?
Answer Posted / manish joshi
1. RTD's: Resistance temperature Detectors : used to
measure the winding temperature , PT-100 is used in RTD and
normally 6Nos can be used
2. BTD's: Used to measure the bearing Temperature rise.
Normally 1pc/Bearing
3. DTT's : Dial type thermometeres with contacts/without
contacts alarm trip
4. Space Heater: Used to remove moisture when motor starts
after a very long time where moisure is present in the
surroundings. ratings 240 V 1Ph.
5. SPM Nipples: for vibration monitoring
6. Seperate terminal box for space heater.
| Is This Answer Correct ? | 25 Yes | 0 No |
Post New Answer View All Answers
i am going to correct power factor of 1600kw induction motor,when i calculate capacitance of capacitor it is three time more in star connection than delta. if motor is star connected which connection i shall adopt for capacitors and reason for adopt this connection
USE OF 8 WAY PAN ASSEMBLY
How can I calculate per unit (KWH) fuel (Gas/ Diesel both) consumption 1MW unit?
what's prime importance of protection in electrical system.if protection system don't work properly what can happen in electrical system?
Where is servomechanism used?
Actually I have a doubt on neutral and earth.we use Ac power without taking neutral by connecting to earth,but at that time does it affects on efficiency of any electrical components or no? If yes how?
why we use copper earthing for neutral while for body GI.
What is reactance, reluctance,capistance, pls give answeer in hinglish and be simply Jo asani we smajh m aa jaye
how to determine the inrush current of a transformer
if negative of DC supply used and positive is grounded through EGB, and if ELCB used in the system then is it sense the positive volatge and get tripped is it possible?
what is lumped and distributed elements?
what is the difference between switchgear and circuit breakers and is there any difference between outdoor and indoor switchgear and circuit breakers , and how would you differentiate between switch yard and substation and grid station . thanks
When will you multiply and devide with derating factors to the actual value while sizing the cable?
why and how current drawn by battery charger depends upon the altitude where it is located?
Where servomechanism is used?