the parts of transformers ?
Answer / amit kumar gupta
Transformer parts are:-
1)BUCHHOLZ RELAY: it is avery sensitive gas and oil
operated instrument which safely detect the formation of
gas or sudden prssure inside the oil transformer.
2)CONSERVATOR: it is used to provide adequate space for the
expansion of oil when transformer is loaded or when ambient
temprature changes.
3)SILICA GEL BREATHER: it sucks the moisture from the air
which is taken by transformer so that dry air is taken by
transformer.
4)DOUBLE DIAPHRAGM EXPLOSION VENT: it is used to discharge
excess pressure in the atmosphere when excess pressure is
developed inside the transformer during loading.
5)OIL LEVEL INDICATOR: it is used to show the oil level in
the transformer.
6) Winding temperature indicator: used to show the
temperature of transformer winding.
7) RADIATORS: these are used for cooling of the transformer
oil.
The supply voltage is connected to the primary
winding, the load is connected to the secondary winding and
in the transformer core only the magnetic flux path will be
established..
In power transformers(used for transmit the heavy
voltages to the grid) on load tap changers used.. but in
distribution transformers off circuit tap changers are
used.
Is This Answer Correct ? | 4 Yes | 3 No |
what is stray capacitance?
PLEASE TELL ME ABOUT QUESTION PAPER OF UPCL ENTERENCE EXAM.
what is formula of illumation calculation
Im designing APFCR Panel for 600 KVAR.I need to calculate the full current so that i can choose the capacity of isolator/Breaker.Kindly suggest with formula.
diff between synchronous gen and alternators
How can I calculate the fault level of a transformer. 1. If fault is 3phase fault 2. If fault is 1phase fault 3. If fault is 2phase fault Dear all geniouses, can you help me by giving answer. If anybody want to send something then mail me at "msalam_shahin@yahoo.com"
what is pulverisation
1.differance between onload ups and off line ups.
In brushless excitation system how generator field current is measure even if the slip rings are absent?
is it necessary to earth the rmu before cutting off the transformer winding?if yes why?
Power Factor Controller
which oil used in transformer?