Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...

the parts of transformers ?

Answer Posted / amit kumar gupta

Transformer parts are:-
1)BUCHHOLZ RELAY: it is avery sensitive gas and oil
operated instrument which safely detect the formation of
gas or sudden prssure inside the oil transformer.
2)CONSERVATOR: it is used to provide adequate space for the
expansion of oil when transformer is loaded or when ambient
temprature changes.
3)SILICA GEL BREATHER: it sucks the moisture from the air
which is taken by transformer so that dry air is taken by
transformer.
4)DOUBLE DIAPHRAGM EXPLOSION VENT: it is used to discharge
excess pressure in the atmosphere when excess pressure is
developed inside the transformer during loading.
5)OIL LEVEL INDICATOR: it is used to show the oil level in
the transformer.
6) Winding temperature indicator: used to show the
temperature of transformer winding.
7) RADIATORS: these are used for cooling of the transformer
oil.

The supply voltage is connected to the primary
winding, the load is connected to the secondary winding and
in the transformer core only the magnetic flux path will be
established..
In power transformers(used for transmit the heavy
voltages to the grid) on load tap changers used.. but in
distribution transformers off circuit tap changers are
used.

Is This Answer Correct ?    4 Yes 3 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

how we can calculate chiller required ampear?

2044


What do you mean by lighting transformer?

1048


State the factors, for the choice of electrical system for an aero turbine.

1162


What are the Formula of computing Back up Time of 500kVA UPS with 4 Battery Banks, each bank composed of 43 pcs of Batteries 12V150Ah. How to compute the Back up Time of UPS? We have also 3X500kVA UPS running in Parallel same composition as I write above.

1341


what is a reactive power? what is the relation with power factor?

2173


There is any especial requirement for motor to drive through with VFD?

2592


Differentiate between ideal and non-ideal voltage sources?

1078


Define resonant peak?

1138


what is the criterion for selecting vector group of Transformers ? i mean how to decide vector group of Generator transformer, substation trasformer and transformer at consumer end

2335


What is dc current source?

1285


1sq mm dc powr cable can carry how much dc currnt

2048


lorteny method

1994


What are PLC leader logic program method

1759


What are the basic components of the feedback control system?

1040


i have 3500 amp load and select current transformer and perches.how i calculate .please understand

2164