Is it possible to run HT motor through LT VFD (LT VFD supply given to Transformer LT side and transformer HT side connected to motor)
Answer / kingshuk dey
To start with, let's get our concepts correct. The motor supply comes from the VFD, which in turn is connected to the power supply from a board (or LT side of transformer, in your case).
Supply(TRF) --> VFD --> Motor
First off lets assume your VFD type is less than or equal to this LT supply. (LT/HT for TRF is subjective, Lt can be 220V when HT is 460V, or 460V when HT is 1000V etc). But a 460V VFD will burn its fuses if connected to 1000V.
Anyway, if you connect the VFD to LT side, and the motor is HT (meaning it's rated for a heavy current like 32KV), the motor will try to pull more and more current to start from the VFD, ultimately exceeding the current setting of the VFD and it will trip with an Overload or Overcurrent (OH, OC) fault on its display. If the current is enough to start the motor, it will rotate, but with very less speed (like if the motor is not connected to any load).
Just as a matter of interest, if you connect the LT side of TRF to VFD, and HT side of TRF to motor, "nothing" will happen as there is no current source (both VFD and motor are current consuming equipments) :P
Motor --> TRF HT -- TRF LT --> VFD (LOL!)
| Is This Answer Correct ? | 1 Yes | 3 No |
Working of microwave oven?
what does the regenerative braking mean?and how it used for Dc motor? thanks.
my 10 hp submersible pump is tripping when connected through ELCB.I have checked the megger value of the coil's with body.It was found to be 0.2mega ohm.that is leakage is there.But when connected to mccb it is not tripping.no leakage current in the motor.Is it safe to connect to mccb? what are the problem's will arise if future?also tell me in ELCB no neutral is connected to motor.than how ELCB was working?
What happens if the Capacitive Voltage Transformer Primary neutral is not earthed. There is a CVT between Transformer and source, and the CVT neutral of the transformer is not earthed, does it effect the transformer while charging or does it effect the transformer charging process.
Why ground terminal is used in pot meter 10k ohms
1. The DC generaror,s induced output emf is connected with a DC motor(as load). when increasing the load of the motor by using brake drum or any way. what are the parameters will changes in both motor and generator(voltage, current, resistance, frequency, speed, torque, power, flux etc...) 2. Similarly for AC generator and AC motor 3. similarly if using DC batteries instead of DC generator, What happens?
How to calculate battery back up time for a 400 AH battery bank installed in telecom shelter for a load of 20 Amps and time taken to fully charge this battery bank?
what is the highest transmission voltage in india???
49 Answers Bhel, EIPL, Engineering, Jindal,
What are the differents between Breaker & Contactor?
for what voltage will reactive power be largest in 380 kv line : a) 375kv b)380kv c)385kv
what are advantage and disadvantage of zener diode?
how to convert star network in delta or vice versa...?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)