When a capcitor is used on 440 v thenthis is kvar rating 25kvar .my question is that when we use this capcitor use 480 v &525 volt .how much kvar increase . Plz give my question ans. And give answer with formula .my mail id is rohitashsaini013@gmail.com
Answer / harish
Q=v*V/X;
X=7.74;
Q IS DIRECTLT PROPORTIONAL TO V*v;
HENCE PERCENTAGE INCREASE IS 480*480-440*440/440*440 =19%
SIMILARLY FOR 525VOLTS THE CHANGE IS 42.36
| Is This Answer Correct ? | 0 Yes | 2 No |
describe the phenomena of vacuum interruption in C.B
why efficiency of generator is greater than motor?
why rating of alternator in kva & induction motor in kw
What will be the minimum megger value of 1700 KVA Transformer? a) Do megger value varies according to climate conditions and area . b) If megger value is 100 mega ohm is it good for new transfomer. Explain?
Sir,In our company there are 3 caterpillar make(capacity:(1) 3.3KV,2.5MW(2)3.3KV,2.5MW & (3)3.3KV,1.9MW) & 1 deutz make (capacity:11KV,3.8MW)gas engines utilised,all are running in paralell. There are three transformer utilised,(1) 6.25MVA,3.3KV/22KV,Impedence voltage:6.7% used for two generator,both are 2.5MW(2)5.5MVA,3.3KV/22KV,Impedence voltage:7.2% used for one generator of 2.5MW & (3) 5.5MVA,11KV/22KV,Impedence voltage:7.8% used for one generator of 2.5MW.all generator breakers capacity of 1250Amps. Sir,I want the details of fault level calculation of generator,transformer individually & for whole system. If you require any information from me.feel free for contact me sir.pl.send the answer of my question as the earliest as possible.
Dear sir, How to calculate 3.5 core pvc aluminium armoured cable meter wise,give with best examples.... please help me in this regards....
how percentage impedence effect on the size of the power transformer?
Hi, I'm running plastic reprocessing company where all motors are running only in delta. Due to that when I use start my 30 hp motor my transformer gets fuse. Where it happens two times a day. I gt a suggestion from a person about Automatic Power Factor Controller APFC. Is it useful for my problem??? Or is der any other way for solving this problem?? Upgrading the transformer is difficult. Pls give Me ur suggestion. Waiting for ur reply.
2 Answers Shree Lingaa Polymer,
what is meant by star/delta voltages as 440/220 in a 3 phase induction motor, and why it should be connected on STAR IN 3 PHASE SUPPLY
how to calculate the ct burden?
I don't understand why when we connect high voltage source in DC to electronic motor , we must add capacitor and resistor in parallel ? (I know that we use capacitor because we want to absorb the current that in the first second electronic motor in opposed with current course produce. ) what are the feature of Resistor and in such situation ?
An 8 pole, 50 Hz, 3-phase IM is loaded to a poing where pull out torque will occur. The rotor resistance per phase is 0.3 ohm and motor stalls at 650 rpm. The rotor frequency at maximum torque point is A 3.33% B 4.44% C 5.55% D 6.66%
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)