how we are desining 63.5 ohm resistor for NGR of alternator?
Answer / vg
to limit the earth fault current generator/Alternator NGR design. ex. for 11KV generator Earth Fault Current to be limit on 100 Amp.
V=I*R
R=V/I
so I=11000/1.732*100=63.5Ohms.
11KV generator NGR 63.5 amps for 100 Amp fault current.
| Is This Answer Correct ? | 8 Yes | 0 No |
why do we prefer -48 volt instead of -24volt or -12 volt etc. ??
why hv winding is not placed near to transformer core
WHAT IS START TO >5HP INDUCTION MOTER IN STAR DELTA METHOD?
- two pumps must work with them at the same time but if the first pump start the second pump must delayed for some time to start also , with motor rated power = 90 KW and rated voltage = 380 V and rated power factor = 0.85 lag please draw the power and control circuit for it and determine all circuit components parameters that you use it
What is the difference between PLC & DCS?
Explain briefly about current , voltage and power
why ups rated in kva
How does HT work & Voltage required?
what is ups?how its works?and what is there in static switch how it works?
how much percentage set in transformer diffrencialrelay
What is VCB? where it is installed at SP. What is SP?
how to reduce shorting current in a slipring induction motor
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)