Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


how can we caliberate interface
level troll

Answers were Sorted based on User's Feedback



how can we caliberate interface level troll..

Answer / jayesh manani

Level troll calibration
0% Zero 100% Span
Liquid Level Displacer out of liquid Displacer in liquid
Interface Level Displacer in lighter liquid Displacer in heavier liquid
Wet Calibration with Water For Liquid level
Zero :
Hang displacer on torque tube arm rod.
Adjust Zero to 3 psi .
Span :
Fill up water into the chamber.
Adjust Span to 15 psi .
0%, 25%, 50% , 75% & 100%. Mark on chamber.
Fill up & Drain water to check 0%, 25%, 50% , 75% & 100%.Check output.
Check function two three times.
Note: Compensate specific gravity difference of water & process liquid.
Process liquid specific gravity is 0.7
Water specific gravity is 1.0
To calibrate level transmitter 100% level.
Water level to be fill up in chamber = 0.7/1.0 x 100 %
= 70 %
Dry Calibration with Weights
Find out Displacer
W = Displacer weight in 2400Gram (2.4 kg)
Specific gravity of process liquid. (WATER)= 1.0
V = Volume of displacer. 1620.84
Displacer diameter 7.620 Centimeter (3 inch).
Length of Displacer 35.56 centimeter (14 inch)
Volume= 3.14 X r² X h
= 3.14 X 3.81 X 3.81 X 35.56
= 1620.84
Zero :
For 0% Hang displacer or 2400 gram weight on torque tube arm rod .
Adjust Zero to 3 psi .
Span :
For 100% Hang weight= Displacer weight – Volume X Specific gravity
= 2400 – 1620 X 1
= 780.
Adjust Span to 15 psi .
Check function two three times for calibration.
Level
%
Hang weight
(Gram)
Transmitter O/P
(PSI)
0 2400 3
25 1995 6
50 1590 9
75 1185 12
100 780 15
For each 25% step subtract 405 Gram weight from hang weight.1620/4=405.
Note: Compensate specific gravity difference of water & process liquid.
Wet Calibration with Water For Interface level
Zero : Displacer in lighter liquid
Process liquid specific gravity is 0.7
Water specific gravity is 1.0
Mark chamber at 70%
Fill up water in chamber.
To calibrate level transmitter 0% level.
Water level to be fill up in chamber = 0.7/1.0 x 100 %
= 70 %
Adjust Zero to 3 psi .
Span : Displacer in heavier liquid.
Process liquid specific gravity is 1
Fill up 100% water into the chamber.
Adjust Span to 15 psi .
Dry Calibration with Weights
Find out Displacer
W = Displacer weight in 2400Gram (2.4 kg)
Specific gravity of process liquid. Oil= 0.7
V = Volume of displacer. 1620.84
Displacer diameter 7.620 Centimeter (3 inch).
Length of Displacer 35.56 centimeter (14 inch)
Volume= 3.14 X r² X h
= 3.14 X 3.81 X 3.81 X 35.56
= 1620.84
Zero : Displacer in lighter liquid
For 0% Hang weight on torque tube arm rod .
Hang weight= Displacer weight – Volume X Specific gravity
= 2400 – 1620 X 0.7
= 2400 - 1134
= 1266
Adjust Zero to 3 psi .
Span : Displacer in heavier liquid.
For 100% Hang weight= Displacer weight – Volume X Specific gravity
= 2400 – 1620 X 1
= 780
Adjust Span to 15 psi .
Check function two three times for calibration.
Level
%
Hang weight
(Gram)
Transmitter O/P
(PSI)
0 1266 3
25 1145.5 6
50 1023 9
75 901.5 12
100 780 15
For each 25% step subtract 121.5 Gram weight from hang weight.(1620-
1134=486)
486/4=121.5.

Is This Answer Correct ?    68 Yes 8 No

how can we caliberate interface level troll..

Answer / mohammad reyaz a nsari

Interface level troll means: When a vessel is filled with
two liquids of two different specific gravities the level
measurement refers to as interface level.
DP = H (D - d)


Calculation # 1 If the calibrating liquid is water:
Process Liquid Density / 1* Displacer height = mm of H2O.

Calculation # 2 If the calibrating liquid is other liquid:
Process Liquid Density / Calibrating liquid density *
Displacer height = mm of H2O. (Calibrating liquid height in
mm).


1. First close both the primary isolation valves and drain
the liquid inside the chamber.
2. Adjust the zero to get 0% output.
3. Connect a transparent PVC tube to the drain point as
shown in hook up.
4. Fill it to the center of the top flange.
5. Adjust the specific gravity or span adjustment
(Electronic Level).
6. Fill it up to 50 %, check linearity.

40. How will you calibrate on interface level control. ?
On an interface leveltrol there are two liquid of two
different specific gravities.
1. The level will be zero when it is full of lighter liquid.
Zero % level = H X d.
H = Displacer length
d = Specific gravity of lighter liquid.
2 The level will be 100 % when it is full of heavier liquid.
100 % level = H X D.
D = Specific gravity of heavier liquid.
Calibration with water:
1. Fill H X d level with water adjust zero.
2. Fill H X D level with water adjust Sp. gravity or span.
3. Check linearity.

Displacer length: L in mm
Density Low : dl in Kg / 1
Density High : DH in Kg / 1
Alarm / Trip point %: X
HH Trip Point: Y in mm

Is This Answer Correct ?    55 Yes 10 No

Post New Answer

More Instrumentation Interview Questions

What is the Temperature Co-officient of Resistance of PT- 1000 and PT-2000 ?

2 Answers   Adani, Birla, MEIL,


What does a hookup diagram look like? can you give sample drawing. thanks.

1 Answers  


on interface level transmitter model(RTG3302-EMERSON) What is threshold valve how can we select correct threshold value T1,T2,T3,T4 When interface water & hydro carbon

0 Answers  


Hello-I know this not an engineering question,I am working in gulf & i want to do correspondence diploma in instrumentation,can any one give me the address of any university in which this courses are available.

2 Answers  


Can I put my meter across an RTD to check it safely witout tripping the equipment when it is connected to an monitoring device eg.RTD module or IQ 1000

1 Answers  


why the SCAN time of DCS is more & that of PLC is less? if the SCAN time of DCS then why we use DCS.

4 Answers  


WHAT IS THE Differance b/w on/off & pid control valve?

10 Answers  


How can corrosion alter the accuracy and precision of a C- Bourdon tube pressure gauge?

1 Answers  


A temperature sensor (RTD) connected via a temperature transmitter is adjusted to give an output of 4ma at 60 deg and 20 ma at 600 deg. This output (4-20ma) from the transmitter is connected to an IGBT-inverter to control a high speed (-12,000 to +12,000 RPM) DC motor. And in the inverter it is programmed as, for 4ma the motor speed will be -3,000 RPM and for 20ma the motor speed will be +10,000 RPM. The question is : If the motor speed is +5,500 (RPM), what will be the temperature? (-sign indicates that the motion is in reverse direction).

9 Answers  


Which standard of hazardous area classification used in India?

1 Answers   Orchid,


what is RPI and NUT in controlnet networx. what happen if we are increase the NUT of controlnet networx?

1 Answers   Schneider,


If we increase D what will be the controller action?

2 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)