how can we caliberate interface
level troll

Answers were Sorted based on User's Feedback



how can we caliberate interface level troll..

Answer / jayesh manani

Level troll calibration
0% Zero 100% Span
Liquid Level Displacer out of liquid Displacer in liquid
Interface Level Displacer in lighter liquid Displacer in heavier liquid
Wet Calibration with Water For Liquid level
Zero :
Hang displacer on torque tube arm rod.
Adjust Zero to 3 psi .
Span :
Fill up water into the chamber.
Adjust Span to 15 psi .
0%, 25%, 50% , 75% & 100%. Mark on chamber.
Fill up & Drain water to check 0%, 25%, 50% , 75% & 100%.Check output.
Check function two three times.
Note: Compensate specific gravity difference of water & process liquid.
Process liquid specific gravity is 0.7
Water specific gravity is 1.0
To calibrate level transmitter 100% level.
Water level to be fill up in chamber = 0.7/1.0 x 100 %
= 70 %
Dry Calibration with Weights
Find out Displacer
W = Displacer weight in 2400Gram (2.4 kg)
Specific gravity of process liquid. (WATER)= 1.0
V = Volume of displacer. 1620.84
Displacer diameter 7.620 Centimeter (3 inch).
Length of Displacer 35.56 centimeter (14 inch)
Volume= 3.14 X r² X h
= 3.14 X 3.81 X 3.81 X 35.56
= 1620.84
Zero :
For 0% Hang displacer or 2400 gram weight on torque tube arm rod .
Adjust Zero to 3 psi .
Span :
For 100% Hang weight= Displacer weight – Volume X Specific gravity
= 2400 – 1620 X 1
= 780.
Adjust Span to 15 psi .
Check function two three times for calibration.
Level
%
Hang weight
(Gram)
Transmitter O/P
(PSI)
0 2400 3
25 1995 6
50 1590 9
75 1185 12
100 780 15
For each 25% step subtract 405 Gram weight from hang weight.1620/4=405.
Note: Compensate specific gravity difference of water & process liquid.
Wet Calibration with Water For Interface level
Zero : Displacer in lighter liquid
Process liquid specific gravity is 0.7
Water specific gravity is 1.0
Mark chamber at 70%
Fill up water in chamber.
To calibrate level transmitter 0% level.
Water level to be fill up in chamber = 0.7/1.0 x 100 %
= 70 %
Adjust Zero to 3 psi .
Span : Displacer in heavier liquid.
Process liquid specific gravity is 1
Fill up 100% water into the chamber.
Adjust Span to 15 psi .
Dry Calibration with Weights
Find out Displacer
W = Displacer weight in 2400Gram (2.4 kg)
Specific gravity of process liquid. Oil= 0.7
V = Volume of displacer. 1620.84
Displacer diameter 7.620 Centimeter (3 inch).
Length of Displacer 35.56 centimeter (14 inch)
Volume= 3.14 X r² X h
= 3.14 X 3.81 X 3.81 X 35.56
= 1620.84
Zero : Displacer in lighter liquid
For 0% Hang weight on torque tube arm rod .
Hang weight= Displacer weight – Volume X Specific gravity
= 2400 – 1620 X 0.7
= 2400 - 1134
= 1266
Adjust Zero to 3 psi .
Span : Displacer in heavier liquid.
For 100% Hang weight= Displacer weight – Volume X Specific gravity
= 2400 – 1620 X 1
= 780
Adjust Span to 15 psi .
Check function two three times for calibration.
Level
%
Hang weight
(Gram)
Transmitter O/P
(PSI)
0 1266 3
25 1145.5 6
50 1023 9
75 901.5 12
100 780 15
For each 25% step subtract 121.5 Gram weight from hang weight.(1620-
1134=486)
486/4=121.5.

Is This Answer Correct ?    68 Yes 8 No

how can we caliberate interface level troll..

Answer / mohammad reyaz a nsari

Interface level troll means: When a vessel is filled with
two liquids of two different specific gravities the level
measurement refers to as interface level.
DP = H (D - d)


Calculation # 1 If the calibrating liquid is water:
Process Liquid Density / 1* Displacer height = mm of H2O.

Calculation # 2 If the calibrating liquid is other liquid:
Process Liquid Density / Calibrating liquid density *
Displacer height = mm of H2O. (Calibrating liquid height in
mm).


1. First close both the primary isolation valves and drain
the liquid inside the chamber.
2. Adjust the zero to get 0% output.
3. Connect a transparent PVC tube to the drain point as
shown in hook up.
4. Fill it to the center of the top flange.
5. Adjust the specific gravity or span adjustment
(Electronic Level).
6. Fill it up to 50 %, check linearity.

40. How will you calibrate on interface level control. ?
On an interface leveltrol there are two liquid of two
different specific gravities.
1. The level will be zero when it is full of lighter liquid.
Zero % level = H X d.
H = Displacer length
d = Specific gravity of lighter liquid.
2 The level will be 100 % when it is full of heavier liquid.
100 % level = H X D.
D = Specific gravity of heavier liquid.
Calibration with water:
1. Fill H X d level with water adjust zero.
2. Fill H X D level with water adjust Sp. gravity or span.
3. Check linearity.

Displacer length: L in mm
Density Low : dl in Kg / 1
Density High : DH in Kg / 1
Alarm / Trip point %: X
HH Trip Point: Y in mm

Is This Answer Correct ?    55 Yes 10 No

Post New Answer

More Instrumentation Interview Questions

How Control valve sizing is done?

3 Answers  


what is the minimum power (P=VI)to produce a spark?

1 Answers  


what is meant by nuclear power plant?

1 Answers  


what is function test.

1 Answers   Takreer,


what is XV and KV valves?

4 Answers  


1)why we are using mostly Ultrasonic Flow meters to measure flow, rather than Radar waves? 2)why we are using Ultrasonic waves and Radar waves to measure the Level?

1 Answers   NTPC,


How a pH sensor & analyzer work at waste water treatment plant, whats the principle & science is beyond this,How pH sensor sence & convert signal & move toward analyzer & analyzer show reading in percent? also what is temperature compensate option in analyzer

1 Answers  


How to work temperature gauge?

1 Answers   KJS,


what is absolute pressure, gauge pressure and atmospheric pressure?

2 Answers   Mother Dairy,


why are use only 4 to 20ma. signal.

9 Answers   Otsuka,


How does your previous experience relate to the job you are applying for ?

1 Answers  


whats diffeence between dcs & scada operation.

3 Answers   Orchid, Reliance,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)