what's the different between ELCB, ELR and ELS?
Answer / asif mansoori
All 3 devices are used for protection from Earth Faults.
Earth Leakage Circuit Breaker is used for putting the circuit off in case any residual current passes out of the circuit & the difference is more than the rating of leakage current, e.g. 300mA, the circuit breaker will go off or cause the main circuit breaker to trip. Usually ELCB is comprising of one main circuit breaker and leakage breaker.
Nowadays, MCB+RCCB acts as RCBO or ELCB. If you use RCCB alone, only protection from leakage current is achieved, if you use both MCB & RCCB, then you get protection from both overload, short circuit and leakage.
ELR is earth leakage relay which is available standalone relay with dry contacts for externally tripping the main circuit breaker.
ELS is also type of ELR, but this is sensor & rating of this is lesser than ELR. For smaller leakage currents, ELS is used.
ELCB-Earth Leakage Circuit Breaker
ELR- Earth Leakage Relay
ELS- Earth Leakage Sensor
| Is This Answer Correct ? | 33 Yes | 2 No |
What is given by the definition in BIL IMP/PF = 950/395 kV. This was found in a name plate of a power transformer.
Advantages of using bundled conductors ?
Why not LED burn after showing alarm,as Alarm volt is 11- 13,But LED is of3 volt,why it isnt Burn??
Why Power generation in India is at 50Hz while in America its 60Hz so is there any advantage/Disadvantage of this ??
38 Answers Australia Visa, College School Exams Tests, Fiat, InfoPlus, L&T, NTPC, TCS,
what happen as when voltage drop(or may decrease) ? in case of atomic base theory?
Witch do depand of Power factor and theory of power factor?
how to reduce shorting current in a slipring induction motor
which protection are used for turbo generator in thermal power plant.
what happenes if two voltage source connected in parallel will be connected to load.
can we load Power capicitors on DG sets?
14 Answers Neptune, Nimbus, Westin,
We use ungrounded DC system (220V/110V) for control and protection system in substations etc. Suppose we have long 2 core DC cables running from our DCDB in control room to the load (length of around 2 to 3 km). Do we need to protect these long DC cables from earth leakages or not? If yes how?
A 12.5 hp slip ring motor taking high initial current and its MPCB is getting open.what may be the reason?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)