what's the different between ELCB, ELR and ELS?
Answer Posted / asif mansoori
All 3 devices are used for protection from Earth Faults.
Earth Leakage Circuit Breaker is used for putting the circuit off in case any residual current passes out of the circuit & the difference is more than the rating of leakage current, e.g. 300mA, the circuit breaker will go off or cause the main circuit breaker to trip. Usually ELCB is comprising of one main circuit breaker and leakage breaker.
Nowadays, MCB+RCCB acts as RCBO or ELCB. If you use RCCB alone, only protection from leakage current is achieved, if you use both MCB & RCCB, then you get protection from both overload, short circuit and leakage.
ELR is earth leakage relay which is available standalone relay with dry contacts for externally tripping the main circuit breaker.
ELS is also type of ELR, but this is sensor & rating of this is lesser than ELR. For smaller leakage currents, ELS is used.
ELCB-Earth Leakage Circuit Breaker
ELR- Earth Leakage Relay
ELS- Earth Leakage Sensor
| Is This Answer Correct ? | 33 Yes | 2 No |
Post New Answer View All Answers
Dear Respected sir how to test ABB REX521 protection relay by relay tester.
Briefly describe means used by electricity suppliers to influence the flow of active and reactive power in power networks (one for each type)?
what is settable hystersis protection? If any body knows plz kindly post the answer..
what is the maximim current drawn by 1 phase and three phase welding machine
How DC earth leakage currents can be reduced ?
IF HT CAPACITOR IN ON POSITION IS THERE ANY LOSSES I.S I SQURE OCCURS IN THE SYSTEM
what is the significance of tan&delta and how it performed in power transformer
What is the formula to calculate the rating of a three phase miniature circuit breaker
WHAT IS counter flux IN CT?
why and how voltage sharing in transformer, during magnetic balance test ?
How to measure size of cable on a given load
why 1.7Uo for HV cable Hi pot test?IE standard why?
diff b/w elcb and rccb
What is vacuum circuit breaker.define with cause and where be use it device?
why impedance relay is used for medium transmission line protection