why we are using ungrounded RTD sensor and what is difference
between grounded RTD and Ungrounded?
Answer / carl_ellis
Show me a 'grounded RTD'. I have never seen a commercial
grounded RTD. The probability of a measurement error due to a
ground loop is too high.
An RTD measurement requires a stable, constant current
source, which is generated by the sensing circuit. If an RTD
element were grounded, a ground loop could affect the current
source depending on the difference in ground potentials at the
RTD element and the sensing circuit. That would create an error
in the measurement.
Grounded thermocouples work some of the time, but other
times some form of isolation is needed because of a ground loop
issue with a thermocouple.
You use ungrounded RTDs because that's the best way for them
to function.
Carl Ellis
Measure First
Is This Answer Correct ? | 4 Yes | 0 No |
if the t/c o/p is 4-20mv then how plc recognize it because we are dealing with the 4-20ma in the plc ????????????????
, Instrument Index, P&ID review, I/O schedule, datasheet, DCS / Analyzers specifications, loop diagrams, hook-up drawings.
Control valve Flow characteristic. How the equal percentege curve form?
What safety precautions you will adopt to work on Steam service control valve?
what is the electrical operation procedure for switching on 27.6MVA electric furnace.
What is DCS?
4 Answers GAIL, Sabic, Trident, Yokogawa,
How to calibration of vibration probe
1 Answers Mina Al Ahmadi Refinery,
A differential transmitter is calibrated to measure the flow of lquied, explain what wil happen if the fluid is not pure but contains some bubble?
how to calibrate temprature switch and flow switch ?
hello i'am samad.Any one Can help me! How to calibrate Vaccum Transmitter DP Type range 0 - 50 mbar abs by hand pump calibrator.
What is a PID?
GIVE THE TEMPERATURE RANGE OF PLATIUM RESISTANCE THERMOMETER.