Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


yogokowa field bus system transmitter all's we are geting
IOP fault in Contiunes please help me fine how we can
normal the broblems?

Answers were Sorted based on User's Feedback



yogokowa field bus system transmitter all's we are geting IOP fault in Contiunes please help..

Answer / nileshkumar jambukiya

1)IOP means input open, when process velue (PV) is out of
renge (20 ma) then IOP alrm comes,

2)when PV is small then minimum range (LRV) less then 4ma
then IOP- alrms come,

3)when cable short or open from loop then same alarm come
iop-,

Is This Answer Correct ?    33 Yes 3 No

yogokowa field bus system transmitter all's we are geting IOP fault in Contiunes please help..

Answer / osagie

IOP Faults are very common in any Yokogawa Fieldbus setup.

As rightly stated in Ans 1, it means Input Open. The idea here is that there is an open circuit somewhere. The circuit here may be the physical circuit or the logical circuit. By logical circuit, I mean the control drawings.

Now lets look are typical scenarios and solutions:

1. Transmitter input over ranged: For a transmitter that is supposed to transmit up to 100%, if its getting a 110% input, it goes on IOP (+) but you will not see the + most times. Under ranged transmitter would give IOP-.
Solution: Get the transmitter input back to the normal range.

2. Consider a control loop with a transmitter input to a controller. whenever the transmitter fails, the controller will give an IOP fault i.e reporting that its input is open - in this case, check the transmitter and possibly change it if bad.

3. Sometime control valves give IOP when they are faulty.

4. Loop component failures can also cause IOP. Check components like the Mega blocks, connectors etc

In general, initial troubleshooting will be re-downloading the control drawing. You can also perform reconfiguration of the Fieldbus devive.

Hope this clarifies.

Osagie.

Is This Answer Correct ?    8 Yes 0 No

yogokowa field bus system transmitter all's we are geting IOP fault in Contiunes please help..

Answer / jigaranadkat

1) Infield bus system, IOP detection is different from HART system.
2) IOP will occur only for input e.g. transmitters.
3) One probability is there (which is most common) that your transmitter is under-ranged or PV value fluctuates highly (on wither ends). Being s digital system you will not receive IOP(-) in FF system.
4) Check for alarms and run integrity test (via PRM) and check if any of the internal blocks like AI or Transducer block or Resource Block is going to OOS (Out of service or Manual Mode).
5) Additional Check :

Check if you are receiving CNF error. If it comes then you may reset the transmitter by removing the power or isolating it from Loop.
This shall resolve the error. If not then you need to replace the transmitter.

Hope this helps.

Is This Answer Correct ?    3 Yes 0 No

yogokowa field bus system transmitter all's we are geting IOP fault in Contiunes please help..

Answer / abdulcader

FF device signal is a communication signal.If any noise or jetter valve are high.it will affect the total segment and time to time particular segment's all devices will go iop.

We can diagnosis the problem by using FFADM[FFadvanced diagnosis module] or fieldbus monitoring device FBT6.

Mostly diagnosis noise valve high in barrier.If you replace the barrier 90% problem will solve.  

Is This Answer Correct ?    2 Yes 0 No

Post New Answer

More Instrumentation Interview Questions

temptrure me ketne frequiency hote hai

0 Answers   ME,


why 4-20 mA signal is preferred over a 0-10V signal

17 Answers   Sofcon,


EXPLAIN SOME IMP QUESTIONS AND ANSWERS ON TOPIC ELECTRONICS,INSTRUMENTATION.........

1 Answers   ONGC,


which flow meter is use for measuring the open channel flow?

2 Answers  


What Is Pre- Commissioning Package +what is DCS & ESD Pre- Commissioning for Instruments Please explain your answer on practical ground base

0 Answers  


what is difference between HOT permit and cold permit

0 Answers   Petro Rabigh,


Before erect the instrument what should you do?

3 Answers   L&T,


Can anyone send most commonly asked interview question in Oil & Gas industry

0 Answers  


How to calibrate the magnetic flow meter and how to correct the flow if it is showing more flow.

5 Answers   Bohra Industries Limited, TCL,


An equipment is certified for EEX, IA, IIC, T6, what do you under stand by this.

3 Answers   ADMA OPCO,


Why do we go for 4-20mA? why not other standara?

6 Answers  


what is meant by nuclear power plant?

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)