Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


yogokowa field bus system transmitter all's we are geting
IOP fault in Contiunes please help me fine how we can
normal the broblems?

Answers were Sorted based on User's Feedback



yogokowa field bus system transmitter all's we are geting IOP fault in Contiunes please help..

Answer / nileshkumar jambukiya

1)IOP means input open, when process velue (PV) is out of
renge (20 ma) then IOP alrm comes,

2)when PV is small then minimum range (LRV) less then 4ma
then IOP- alrms come,

3)when cable short or open from loop then same alarm come
iop-,

Is This Answer Correct ?    33 Yes 3 No

yogokowa field bus system transmitter all's we are geting IOP fault in Contiunes please help..

Answer / osagie

IOP Faults are very common in any Yokogawa Fieldbus setup.

As rightly stated in Ans 1, it means Input Open. The idea here is that there is an open circuit somewhere. The circuit here may be the physical circuit or the logical circuit. By logical circuit, I mean the control drawings.

Now lets look are typical scenarios and solutions:

1. Transmitter input over ranged: For a transmitter that is supposed to transmit up to 100%, if its getting a 110% input, it goes on IOP (+) but you will not see the + most times. Under ranged transmitter would give IOP-.
Solution: Get the transmitter input back to the normal range.

2. Consider a control loop with a transmitter input to a controller. whenever the transmitter fails, the controller will give an IOP fault i.e reporting that its input is open - in this case, check the transmitter and possibly change it if bad.

3. Sometime control valves give IOP when they are faulty.

4. Loop component failures can also cause IOP. Check components like the Mega blocks, connectors etc

In general, initial troubleshooting will be re-downloading the control drawing. You can also perform reconfiguration of the Fieldbus devive.

Hope this clarifies.

Osagie.

Is This Answer Correct ?    8 Yes 0 No

yogokowa field bus system transmitter all's we are geting IOP fault in Contiunes please help..

Answer / jigaranadkat

1) Infield bus system, IOP detection is different from HART system.
2) IOP will occur only for input e.g. transmitters.
3) One probability is there (which is most common) that your transmitter is under-ranged or PV value fluctuates highly (on wither ends). Being s digital system you will not receive IOP(-) in FF system.
4) Check for alarms and run integrity test (via PRM) and check if any of the internal blocks like AI or Transducer block or Resource Block is going to OOS (Out of service or Manual Mode).
5) Additional Check :

Check if you are receiving CNF error. If it comes then you may reset the transmitter by removing the power or isolating it from Loop.
This shall resolve the error. If not then you need to replace the transmitter.

Hope this helps.

Is This Answer Correct ?    3 Yes 0 No

yogokowa field bus system transmitter all's we are geting IOP fault in Contiunes please help..

Answer / abdulcader

FF device signal is a communication signal.If any noise or jetter valve are high.it will affect the total segment and time to time particular segment's all devices will go iop.

We can diagnosis the problem by using FFADM[FFadvanced diagnosis module] or fieldbus monitoring device FBT6.

Mostly diagnosis noise valve high in barrier.If you replace the barrier 90% problem will solve.  

Is This Answer Correct ?    2 Yes 0 No

Post New Answer

More Instrumentation Interview Questions

what is puling in n pulling out in flame scanner system?

1 Answers  


Lux meter is the measuring device to measure the lux level of lighting fixture. in industrial sector two types of lighting fixture is being used as street lighting purpose 1. HPSV (Sodium) and 2. HPMV (Mercury). HPMV having white light which is an combination of red, blue and yellow colour, while HPSV haivng Yellow lighting. in HPSV red & blue colour will be absent. during measurement of the lux level of HPSV and HPMV fixture. 1. Lux meter can measure the actual lux level of both fixture? 2. or it will show false reading for HPSV fixture light as it has only yellow light present. please give me answer

0 Answers   Ace Info,


what is isloted barrier how it works and what are the main purpose.how it make safe area.

0 Answers  


what will the sending unit in the fuel gauge utilizes?

0 Answers  


if drum level is low what is interlock? i mean we put interlock to fd fan or id fan ?

4 Answers  


What is PLC(programmable logic control)?

1 Answers  


How to calibrate RC Feeder system in thermal power station?,If any instrument available to calibrate it,ple inform me. make:stock,

0 Answers   TATA,


can we replace a slot sensor (inductive type) with limit switch (potenial free contact / no-nc type).

0 Answers   Max India,


How to calibrate the control valve.

1 Answers  


wht is dcs architecture ? can u give example?

3 Answers  


WHAT ARE MAIN DIFFERENCE BETWEEN DCS AND SCADA?

7 Answers   ABB, Gold Fields, Rand Water,


HI FRIENDS IHAVE QUESTION 1.WHAT IS PARTIALSTROKE TEST?WHY IT IS USED ON ESD ON OFF VALVES?

3 Answers   KNPC,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)