yogokowa field bus system transmitter all's we are geting
IOP fault in Contiunes please help me fine how we can
normal the broblems?
Answers were Sorted based on User's Feedback
Answer / nileshkumar jambukiya
1)IOP means input open, when process velue (PV) is out of
renge (20 ma) then IOP alrm comes,
2)when PV is small then minimum range (LRV) less then 4ma
then IOP- alrms come,
3)when cable short or open from loop then same alarm come
iop-,
| Is This Answer Correct ? | 33 Yes | 3 No |
IOP Faults are very common in any Yokogawa Fieldbus setup.
As rightly stated in Ans 1, it means Input Open. The idea here is that there is an open circuit somewhere. The circuit here may be the physical circuit or the logical circuit. By logical circuit, I mean the control drawings.
Now lets look are typical scenarios and solutions:
1. Transmitter input over ranged: For a transmitter that is supposed to transmit up to 100%, if its getting a 110% input, it goes on IOP (+) but you will not see the + most times. Under ranged transmitter would give IOP-.
Solution: Get the transmitter input back to the normal range.
2. Consider a control loop with a transmitter input to a controller. whenever the transmitter fails, the controller will give an IOP fault i.e reporting that its input is open - in this case, check the transmitter and possibly change it if bad.
3. Sometime control valves give IOP when they are faulty.
4. Loop component failures can also cause IOP. Check components like the Mega blocks, connectors etc
In general, initial troubleshooting will be re-downloading the control drawing. You can also perform reconfiguration of the Fieldbus devive.
Hope this clarifies.
Osagie.
| Is This Answer Correct ? | 8 Yes | 0 No |
1) Infield bus system, IOP detection is different from HART system.
2) IOP will occur only for input e.g. transmitters.
3) One probability is there (which is most common) that your transmitter is under-ranged or PV value fluctuates highly (on wither ends). Being s digital system you will not receive IOP(-) in FF system.
4) Check for alarms and run integrity test (via PRM) and check if any of the internal blocks like AI or Transducer block or Resource Block is going to OOS (Out of service or Manual Mode).
5) Additional Check :
Check if you are receiving CNF error. If it comes then you may reset the transmitter by removing the power or isolating it from Loop.
This shall resolve the error. If not then you need to replace the transmitter.
Hope this helps.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / abdulcader
FF device signal is a communication signal.If any noise or jetter valve are high.it will affect the total segment and time to time particular segment's all devices will go iop.
We can diagnosis the problem by using FFADM[FFadvanced diagnosis module] or fieldbus monitoring device FBT6.
Mostly diagnosis noise valve high in barrier.If you replace the barrier 90% problem will solve.
| Is This Answer Correct ? | 2 Yes | 0 No |
what is the principal of coriolis mass flowmeter
dear friends pls tell me how temperature compensations are done in bourdoun tube of pressure guages thankx
PLZ explain to me massflow
How to derive IO Count (AI, AO, DI and DO ) from a Field instrument (FI) Bill of Quantities (BOQ) given by client.
Name some of the common protocol use in automation.
How to check range of DP Transmitter
Can u tell me the principle of the tc,rtd,level switch,pressure switch ,transmitter(pr flow level temp.),vibration...plz
on which principle control valve works?
In most instances, Inertia processes are quite uncommon. Give an example of a combined Resistance and Capacitance situation.Describe an application, which according to your understanding of the subject matter, comprises of both Resistance and Capacitance effects.
How to ensure vibration sensor functioning accordingly.With out using an other sensor.
any questions on motor and energy conversions machines?
Q- Which of the following is Close loop system - a-)respiratory System b-)traffic light system c-)washing machine d-)Room heater my option is A, what is our take on option B & C
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)