Is it possible to make 0.75KW motor earthing from MCC panel by
using the 1.5 SQMM, 4 core cable, means 3 core for 3 Phases &
1 core for Earth terminal?
Answers were Sorted based on User's Feedback
Answer / najam sultan
For earthing we don't need to use 4 cores, only a single core is enough for earthing.And 1.5sqmm single core cable is enough for earthing of 0.75 kW motor.
| Is This Answer Correct ? | 4 Yes | 3 No |
Answer / avd
Yes it can be done.Do not worry for fault level because it
will be greaty reduced due to lowersize cable.But make sure
you have installed earth fault protection device to isolate
incase of earth fault.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / mukesh
For motor we need to use 3 cores, only a single core is
enough for earthing.And 1.5sqmm single core cable is enough
for earthing of 0.75 kW motor and double earth is
requirements for whereas 3 phases is used as per rule.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / jyotiranjan sahoo
Yes it can use 1.5 sqmm cable of earthing for that motor but in Indian standard we must be use another body earthing
| Is This Answer Correct ? | 0 Yes | 0 No |
What id difference between power and energy?
difference between EMVT, PT & CVT ?
what are the energy savings methods that are existing in coal based power plant?
Why we are using Isolation Power Transformer inplace of commercial power transformer? What's the difference between them?
What is the ladder circuit?
1 Answers Mitharg Information Systems,
How neutral voltage for transformer decided? eg 33kv neutral voltage for 200MVA transformer?
we have amp, voltage, kw, length detail then how to calculte copper & alluminium size of conductor of 3-phase induction motor
When calculating the speed of a rotor required for a particular frequency of synchronous generator we use the equation 60f/p Is this p is the number of pole pairs of rotor & do we consider the number of pole pairs in the stator is 1?
What is the effect of using an underrated size cable to supply electrical power to a 3 phase ac electrical motor? What is the effect of using an overrated size cable for the same motor?
what are the types of basic earthing?and why we are doing that?
The inexpensive way to improving energy efficiency of a motor which operates consistently at below 40% of rated capacity is by _____.
What is the Maximum Power generation capacity of a Synchronus Machine ??
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)