Different between megger and contact resistance meter
Answers were Sorted based on User's Feedback
Answer / yousaf ali
Megger also called Hipot (high potential) test is used for
high voltage insulation, while contact resistance meter
measure the resistance of contact of circuit breaker it is
usually in micro ohm.
| Is This Answer Correct ? | 5 Yes | 3 No |
Answer / babu
megger for high resistance measurement(cable insulation)
| Is This Answer Correct ? | 3 Yes | 2 No |
Answer / anwar
Meggar used to measure cable resistance,conductor
continuity,phase identification,etc..
where as contact resistance meter used to measure low
resistcance like relays,contactors.
| Is This Answer Correct ? | 0 Yes | 2 No |
for 4 MVA , 33K.V/6.6K.V transformer. secondary side the connected load is 3000H.P. What is the rating of capacitor bank to be insttaled.
Advantage of earthing transformer
How to connect surge arrester with equipment?
what is the purpose of reactor in electrical substations ?
How much depth we will take in 33kv sub station and why.
what is impedance of transformer?
7 Answers Synergy, Vijai Electricals,
why 30kva ups buzzing(hamming) sound?
2 Answers Madhya Pradesh Electricity Board MPEB,
What is main difference between earthing and neutral grounding?
what is the difference between DOL starter&star-delta starter& automatic star-delta starter
How to calculate D.C load current?
what is "PE" earthing? and what do u know abt 16mm cable?
What are the voltages at which electrical energy is transmitted
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)