We use ACB in LT and VCB in HT.But if we use VCB in LT and
ACB in HT that what will be the effect on the system or any
power range?
Answers were Sorted based on User's Feedback
Answer / jithin
VCB is designed for HT it has vaccum chamber that prevents arcing and it triping speed is higher
ACB is desined for LT the terminals are almost open to atmospere it can cause flashing if we use it on HT
| Is This Answer Correct ? | 32 Yes | 0 No |
Answer / karna
HT Line Means 6.6KV,11KV and 33KV. LT Line means 415V. So
the ACB are Manufacutered for LT side because , based on
shortcircuit KA busbar terminal are designed in ACB . In HT
line while switching On & OFF ARC will be more it will not
withstand in ACB . IF we use VCB in LT side , the VCB will
not helpfull at fault condition, because its upstream
breaker will trip or component will damage
| Is This Answer Correct ? | 17 Yes | 5 No |
Answer / maurilio
if you use a VCB in low tension it odes not make problems
but if a ACB or Air Circuit Breakers in HT you will see a
lot of ligthning and probably fire in the breaker
So it is no convenient to use a ACB on HT
| Is This Answer Correct ? | 13 Yes | 8 No |
Answer / sushil kumar
Vcb is ht supply use rating of high voltage but acb lt supply used this manufacture 440 voltage difference for relay siting vcb and acb vcb is use closed area but acb use open area
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / hardik
As per Karna ACB is not usfull in HT because of its limited
capacity but in casw of VCB apply in LT it can dafinatly
helping out after making its ragular reliese setting and
tripping in foulty condition is depend on relay... so VCB
we can use but drow back is VCB in LT system it is more
expancive then ACB thats it...
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / kishore
actually acb is made for LT bcz EVERYTHING HAVE A LIMIT,SIMILARLY IF WE USE VCB AT LT THEN NO PRBL BUT IT IS A GREAT ECONOMIC LOSSES FOR US OK.
| Is This Answer Correct ? | 2 Yes | 3 No |
howmany insolaters needed in 66kv line
what is brushless generator.How does work it..??
1. Why transfomer reting in KVA and Motor in HP
11 Answers AirIndia, Jindal, Mind Tree,
If there is unit power factor in a power house and a capacitor bank used in a factory at resistive load . In this case, will there leading power factor in power house across that factory.
what is soft starter?working principle?where it can use?
two 100W/230V bulb are connected in series. what would be the voltage drop across 1 bulb
why dc is not given to transformer
what is the mazor difference between the induction transformer and synchonous motor?what is the similarity between them?
what is the difference between RMS meter and normal meter
how much amps can i connect for 4core 120mm armade cable
What is the function of probe in cro?
what is the other name of dc series motor
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)