how to calibrate temprature switch and flow switch ?
Answer / carl_ellis
The key to 'calibrating' a temperature switch is it is a
switch, it is not a continuous analog sensor. So there's
no need to mess around with a zero and span value, like you
would on temperature transmitter.
All that matters is setting the switch's trip point, the
setpoint, and in some cases, the reset
(deadband/hysteresis) point. There is no need to mess
around anything but the trip point, it's time consuming
enough to get a precise setpoint on switch.
You need to know
- the setpoint
- in some cases, the reset (deadband/hysteresis) point
values
- whether the setpoint (SP) is for a rising or falling
temperature. Because they're mechanical switches, a SP for
falling is NOT same as a SP for rising.
- switch functionality - Does the switch close or open on
rise or fall. There are applications for all the
variations: close on rise, close on fall, open on rise,
open on fall.
Check how to change the setpoint on the switch. Some
switches have a setpoint lock (nut). Some are blind
adjustments, some are adjustments with indicated
temperature values. Some have a separate
deadband/hysteresis adjustment. The latest temperature
switches are digital, and the setpoint and hysteresis reset
point are entered as values.
Many procedures require an actual test with a calibrating
heat/cold (dry block calibrator or oil bath) source and a
temperature "standard" is needed for a reference
temperature, to prove the mechanical setting is correct.
Sometimes the standard is a certified dry block with a
readout, sometimes it's a mercury thermometer, sometimes
its certified RTD with a certified readout. Older cal
equipment has stand-alone electrical equipment, like an
indicator lamp or an ohmmeter that is used to indicate
switch closure on the temp switch, more modern cal
equipment has built-in connections and an indicator for
that.
Make the setpoint adjustment, run the temperature source,
heat or cool, and note the trip and reset points. If
needed, make adjustments and re-run the test until the
setpoint (and reset point) are within the spec needed.
Record the results, put a cal sticker or tag on the beast,
and you're on to the next one.
Tell 'em Carl sent you.
| Is This Answer Correct ? | 8 Yes | 1 No |
1.how can calibration temperature transmitter and flow transmitter? 2.
define optical temperature detector
hi all plz tell me difrence between analog or digital load cell.
key phaser where is use and work
types of transformer.. 1ph 3ph or core shell?
how to calibrate control valves & power cylinders & ultra sonic level transmitters
Draw a simple circuit for a well head control panel used to protect the well against fire, leak, blockage, ESD, & controls the operation of one downhole & one surface safety valve. Explain the operation and controls
how pressure reduce through pressure control valve? suppose we have to reduce 20 kg pressure to 10 kg pressure , then what we do ? open the valve or close the valve , initially it is 20 % is upon ( for ur knowledge ).
how to do dynolab wind speed sensor loop test, how to simulate value,i have simulate mA 4-20mA but not responding in DCS faceplate, please kindly advice me any one.
plz you help about Que paper of mahagenco previous your,any model paper relad to it{maharastra power genration}
in my company organisation in plan to take new PLC system for replacing old relay system , for that what I/P needsd to submit to the system house of PLC supplier?
What is defferent betwen ESP &PCP PUMP .HOW IT IS WORK?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)