how to identify 3phase....r y b .A new make altnator how
to identify R
Answers were Sorted based on User's Feedback
On a new alternator the markings are usually U V W N
These match to R Y B N.
But it may be that the phase rotation in the building is
backwards and all the 3 phase motors will then run
backwards on the new alternator supply.
A phase rotation meter should be used to confirm that the
phase rotation is identical.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / b.janardhana rao
Normally we erection the new generator we connect the main supply from DG set to Electrical pane. we charge the panel from DG supply then we check the direction of motors. if it is reversed the we change the polarity of 3 phases. RYB to change RBY.
Is This Answer Correct ? | 0 Yes | 1 No |
why current is leading in capacitor?
what is Micrologic 6.0A advantages over Micrologic 2.0A
how to calculate the minimum permissible limts of insulation resistance of switchyard equipments
DEAR SIR, HOW TO CALCULATE WELDING TRANSFORMER CAPACITY IN KW OR KVA (POWER). TWO WELDING TRANSFORMER USED WHAT TYPE OF DG SET CAPACITY LIKE ( 45 KVA OR 62.5 KVA), PLEASE TELL THE WELDING TRANSFORMER RATEINGS. I AM REFINARY (TANKS WELDING) THANKING YOU
HOW many type of Circut Breaker in the world used in 400 kv substation?
Generally in d.c. circuits the direction of current is from possitive to negative.In a.c.circuits what is the direction fo current flow
How do you select a cable size(cu&Al)for a particular load?
Wat wil happen if Transformer is operated at 100 HZ Frequency?
In a circuit the power factor was leading what will happen?
1. name the relay for protecting transformer 2. Current Transformer 3. potential Transformer
iam using DM 3251 voltmeter(1 percent accuracy)for 11KV system PT ratio is 11KV/110V.can anybody explain what is the max and min voltage deviation.
in dc machines in the armature nature of power is ac but why we take rasistance instead of impedance?