Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


Why we are using 4-20 mA as Analog signal transmission
other than 3 to 19 or 2 to 18 or 6 to 22 like wise ? What
is the reason behind using 4 & 20 mA? Can anyone give
proper technical reply ?

Answers were Sorted based on User's Feedback



Why we are using 4-20 mA as Analog signal transmission other than 3 to 19 or 2 to 18 or 6 to 22 li..

Answer / vinoth

the destination of any signal will be a Controller.
Take DCS, its input supply will be 1-5V.
from instruments, across a 250ohm resistor, the value will
reach DCS as desired 1-5V.

expl:
say 4ma is the output of transmitter.
V=IR,
V=4ma * 250 ohm
V= 1V,
say 20ma,
V=20ma*250ohm
V=5V.

Is This Answer Correct ?    10 Yes 1 No

Why we are using 4-20 mA as Analog signal transmission other than 3 to 19 or 2 to 18 or 6 to 22 li..

Answer / dhanabalan

It is where the linearity is maintained (4-20 mA Signal).

Is This Answer Correct ?    9 Yes 1 No

Why we are using 4-20 mA as Analog signal transmission other than 3 to 19 or 2 to 18 or 6 to 22 li..

Answer / t.naveen babu

The reasons for the 4-20 mA standard (and, before it, the
10-50 mA standard) have a lot to do with the original 3-15
psi/20-100 kPa air
signal. The origin of the suppressed or "live" zero in the
pneumatic system was two-fold - if you want to reduce a
passive pneumatic signal quickly, you need to maintain some
differential between the pressure and the "sink" - in this
case, atmospheric air. The basic characteristic of a
flapper-nozzle assembly also has a bit to do with it -
the "linear" range of the flapper pressure is about 3 - 15
psi for a 20 psi supply. Next question - why a 20psi
supply? Anyone else remember 6-30 psi equipment for
final actuators needing a bit more grunt??

The original electronic instruments were direct imitations
of the pneumatic systems with bellows replaced by magnet-
coil assemblies. The first I came across were used in a
geothermal power project (1958 vintage)where the pressure
at the power station was controlled by manipulating valves
in the steam field 1 1/2 miles or so away. The flapper-
nozzle was replaced by a
contact moving between positive and negative terminals - I
guess a bity of mains hum in the amplifier kept it
jittering. In the mid-70's Foxboro produced a range of
pressure transmitters using the magnetic principle which
used the same basic mechanism as their pneumatic equipment -
but the size of the coils made the assemblies a lot
bigger ...

Is This Answer Correct ?    3 Yes 3 No

Why we are using 4-20 mA as Analog signal transmission other than 3 to 19 or 2 to 18 or 6 to 22 li..

Answer / abhishek

this 3-15 psi later used in electronic signal as 4-20mA. 4mA
used as live Zero , & 20mA is current so
20mA*24V=480mWatt. this power if we increase any signal
wire can cause such type of arc that can cause Fire.

Is This Answer Correct ?    4 Yes 4 No

Why we are using 4-20 mA as Analog signal transmission other than 3 to 19 or 2 to 18 or 6 to 22 li..

Answer / ahmad

1- Any electronic circuit having its error, here Ico=3.85 ma(aprox=4 ma). that is why we do start from 4 ma.
2- it is also convertable to 1-5 volt, with precision resistance of 250 ohms.

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Instrumentation Interview Questions

what is the difference between 2 wire and 3 wire RTD- application wise,cost effectivity?

2 Answers  


Hi at present i m wrking with tire industry as a manager having gud ctc. Nw I am selected for 1 of the best chemical industry but my ctc is lower than current n also i hv 2 compromize vit post as post is also lower. I hv 6 yrs of exp in various type of industry. Should i join chemical industry as there ar lot of gud instrument than tire? Financialy i can manage 4 more 2 yrs. Bt during wrking vit tire industry i found there is very less instrument n feel that opportunity is less. Pl ans quickly. I have less time to decide.

1 Answers  


what master plc do?

2 Answers   ISRO, Yokogawa,


Can anybody please let me know Orifice plate sizing calculation formula and step by step procedure

0 Answers  


If range of 3-15 psi, a multiplying relay with a 1:2 ratio would give what output pressure for 6 psi input?

1 Answers  


What is Span Error

0 Answers  


we have a s-5 simense plc having op7 .recently on op7 showing error 1.plc not present 2. DB error frequently. can u have any solution . please send me.

0 Answers  


how to caluculate flow by using transmitter?tell me plz I am eagerly waiting for your reply..

2 Answers   Agi Glaspac, Reliance Power,


Where are use of pressure,level,flow switches?and what is input and output

3 Answers  


one rtd sensor which is connected at middle of distillation column where actual temp. is 100deg but when we tight this sensor at thermowell end it goes down to 90 deg & when remove from the thermowell(but sensor end dipped in well) showing actual reading, what is reason?

3 Answers  


Whatis the reset ofset and control system in instrumentation

0 Answers   Asyad International Company, CAE, Sugar Factory,


What is T4 temperature in compressor?

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)