Why we are using 4-20 mA as Analog signal transmission
other than 3 to 19 or 2 to 18 or 6 to 22 like wise ? What
is the reason behind using 4 & 20 mA? Can anyone give
proper technical reply ?
Answers were Sorted based on User's Feedback
the destination of any signal will be a Controller.
Take DCS, its input supply will be 1-5V.
from instruments, across a 250ohm resistor, the value will
reach DCS as desired 1-5V.
expl:
say 4ma is the output of transmitter.
V=IR,
V=4ma * 250 ohm
V= 1V,
say 20ma,
V=20ma*250ohm
V=5V.
| Is This Answer Correct ? | 10 Yes | 1 No |
Answer / dhanabalan
It is where the linearity is maintained (4-20 mA Signal).
| Is This Answer Correct ? | 9 Yes | 1 No |
Answer / t.naveen babu
The reasons for the 4-20 mA standard (and, before it, the
10-50 mA standard) have a lot to do with the original 3-15
psi/20-100 kPa air
signal. The origin of the suppressed or "live" zero in the
pneumatic system was two-fold - if you want to reduce a
passive pneumatic signal quickly, you need to maintain some
differential between the pressure and the "sink" - in this
case, atmospheric air. The basic characteristic of a
flapper-nozzle assembly also has a bit to do with it -
the "linear" range of the flapper pressure is about 3 - 15
psi for a 20 psi supply. Next question - why a 20psi
supply? Anyone else remember 6-30 psi equipment for
final actuators needing a bit more grunt??
The original electronic instruments were direct imitations
of the pneumatic systems with bellows replaced by magnet-
coil assemblies. The first I came across were used in a
geothermal power project (1958 vintage)where the pressure
at the power station was controlled by manipulating valves
in the steam field 1 1/2 miles or so away. The flapper-
nozzle was replaced by a
contact moving between positive and negative terminals - I
guess a bity of mains hum in the amplifier kept it
jittering. In the mid-70's Foxboro produced a range of
pressure transmitters using the magnetic principle which
used the same basic mechanism as their pneumatic equipment -
but the size of the coils made the assemblies a lot
bigger ...
| Is This Answer Correct ? | 3 Yes | 3 No |
Answer / abhishek
this 3-15 psi later used in electronic signal as 4-20mA. 4mA
used as live Zero , & 20mA is current so
20mA*24V=480mWatt. this power if we increase any signal
wire can cause such type of arc that can cause Fire.
| Is This Answer Correct ? | 4 Yes | 4 No |
Answer / ahmad
1- Any electronic circuit having its error, here Ico=3.85 ma(aprox=4 ma). that is why we do start from 4 ma.
2- it is also convertable to 1-5 volt, with precision resistance of 250 ohms.
| Is This Answer Correct ? | 0 Yes | 0 No |
why in vortex flow transmitter dcs range is configuring less than sensor range. eg (sensor range 500-25000 kg/hr and dcs range 0-24000 kg/hr).
what is the working principle of hydra step(electronic level indicator)?
2 Answers Bengal Energy, Lanco,
In control valve , Failure position : Close If it is Fail close(FC) during failure of AIR.. what will be the initial/ normal position of control valve is it normally open or close? please some one explain soon..
what is a instrumentation ?
types of transformer.. 1ph 3ph or core shell?
Explain pH, Conductivity.
what is three element in thermal boiler
Induction type 1-p wattmeter reads ….. a) true value b) apparent value c)volt ampere value
3 Answers Engineers India Limited,
How to calibrate an pressure gauge with yantrika test bench?
radial & axial vibration sensor output voltage is ac or dc volt?
Determine the manipulated variable, controlled variable, and the measured variable given a description of various typical industrial processes.
why flow transmitter showing 2.2ma?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)