If the load is 10Kw and power factor has to improve from 0.5
to 0.8,how can we select the capacitor rating
accordingly.Illustrate by showing formula?

Answers were Sorted based on User's Feedback



If the load is 10Kw and power factor has to improve from 0.5 to 0.8,how can we select the capacitor..

Answer / guest

at 0.5pf Apparent power is 10/0.5=20VA
reactive power = 17.321kVAR.
At 0.8pf
APPARENT POWER =10/0.8=12.5VA
Reactive power=7.5kVAR
So we need to provide (17.321-7.5)=9.821kVAR reactive power
through capacitor to bring of up 0.8 from 0.5.
So we need a capacitor rated for approximately 10kVAR to
achieve the target.
ANS= CAPACITOR RATING 9.821kVAR (approximately 10 kVAR)

Is This Answer Correct ?    10 Yes 2 No

If the load is 10Kw and power factor has to improve from 0.5 to 0.8,how can we select the capacitor..

Answer / prasad damodar bhoir

kvar= kw (tan phi 1- tan phi 2)
cos phi 1= 0.5, phi 1= cos inverse 0.5= 60
cos phi 2= 0.8, phi 2= cos inverse 0.8= 36.86
kvar= 10 (tan60 - tan 36.86)= 10 (1.73-0.74)
kvar= 9.9

Is This Answer Correct ?    4 Yes 0 No

If the load is 10Kw and power factor has to improve from 0.5 to 0.8,how can we select the capacitor..

Answer / h salim

Load = 10 kW
cos phi 1 = 0.5
cos phi 2 = 0.8

Rating of capacitor Qc = kW(tan phi 1- tan phi 2 )

Is This Answer Correct ?    3 Yes 0 No

If the load is 10Kw and power factor has to improve from 0.5 to 0.8,how can we select the capacitor..

Answer / prakash g.r.

Calculation of Required Kvar

Initial or Present Power Factor =Qi,
Required Power Factor = Qd

KVAr= KW(TANQi-TANQd)

Qi=COS-1PFi = Initial Power Factor Angle

Qd=COS-1PFd = Final Power Factor Angle

Is This Answer Correct ?    3 Yes 0 No

If the load is 10Kw and power factor has to improve from 0.5 to 0.8,how can we select the capacitor..

Answer / ahatesham

at 0.5pf Apparent power is 10/0.5=20VA
reactive power = 17.321kVAR.
At 0.8pf
APPARENT POWER =10/0.8=12.5VA
Reactive power=7.5kVAR
So we need to provide (17.321-7.5)=9.821kVAR reactive power
through capacitor to bring of up 0.8 from 0.5.
So we need a capacitor rated for approximately 10kVAR to
achieve the target.
ANS= CAPACITOR RATING 9.821kVAR (approximately 10 kVAR)

Is This Answer Correct ?    2 Yes 0 No

If the load is 10Kw and power factor has to improve from 0.5 to 0.8,how can we select the capacitor..

Answer / nagesh.patwari

Kvar = KW * [ tan (cos^-1* Current PF) - tan (cos^-1* Required PF)]

Is This Answer Correct ?    0 Yes 0 No

If the load is 10Kw and power factor has to improve from 0.5 to 0.8,how can we select the capacitor..

Answer / lohith

kvar=kva*sin

Is This Answer Correct ?    2 Yes 3 No

If the load is 10Kw and power factor has to improve from 0.5 to 0.8,how can we select the capacitor..

Answer / rk

How did you Calculate Apparent Power=20VA to Reactive power 17.321 KVAR simlarly 12.5VA to 7.5KVAR As the formula is KVAR=KVA/KW

Is This Answer Correct ?    0 Yes 2 No

If the load is 10Kw and power factor has to improve from 0.5 to 0.8,how can we select the capacitor..

Answer / nag

unity powerfactor

Is This Answer Correct ?    0 Yes 5 No

Post New Answer

More Electrical Engineering Interview Questions

What is the effect on in Zone and out zone fault if Phase side CT is Vk/2<30 mA and Neutral side is CT is Vk/4<30 mA for Transformer REF protection

0 Answers   ABB,


how hydrogen or helium is a cooling agent for alternator./ generator of big size.

1 Answers  


In Power cable specification what is U0/U and Um.

0 Answers  


what is difference between ELCB, RCBO & MCB

2 Answers  


how to calculate the neautral earthing conductor size for a 500kva dg set.

2 Answers  






how a single machine can act as both motor and generator? and give explanation interms of connections?

1 Answers  


what is the difference between neutral and earth

11 Answers  


How to synchoronize the generator (with gcb,GT) to grid????? ????? from Grid iam getting power (rated 400kv/20kv) through GT and its goes to UAT.,,ST.,, now my generator(rated 20kv ) ready.,, now iam closing my GCB.,, in GT iam suddenly giving 20kv on that Gt.,, what will happend

0 Answers  


Difference between 3.5 core and 4 core

2 Answers  


Why a Permanent Magnet Generator has higher frequency as compared to frequency of main alternator?

0 Answers  


What is the exact minimum vale of voltage between an earth and netural which can damage or can do malfunction of the electronic equipments ? If this is mentioned in any book, pl.give reference.

0 Answers   Bhushan Power Steel,


how can we connect a distance relay to CT core that is for backup protection or metering?

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)