If the load is 10Kw and power factor has to improve from 0.5
to 0.8,how can we select the capacitor rating
accordingly.Illustrate by showing formula?
Answers were Sorted based on User's Feedback
Answer / guest
at 0.5pf Apparent power is 10/0.5=20VA
reactive power = 17.321kVAR.
At 0.8pf
APPARENT POWER =10/0.8=12.5VA
Reactive power=7.5kVAR
So we need to provide (17.321-7.5)=9.821kVAR reactive power
through capacitor to bring of up 0.8 from 0.5.
So we need a capacitor rated for approximately 10kVAR to
achieve the target.
ANS= CAPACITOR RATING 9.821kVAR (approximately 10 kVAR)
| Is This Answer Correct ? | 10 Yes | 2 No |
Answer / prasad damodar bhoir
kvar= kw (tan phi 1- tan phi 2)
cos phi 1= 0.5, phi 1= cos inverse 0.5= 60
cos phi 2= 0.8, phi 2= cos inverse 0.8= 36.86
kvar= 10 (tan60 - tan 36.86)= 10 (1.73-0.74)
kvar= 9.9
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / h salim
Load = 10 kW
cos phi 1 = 0.5
cos phi 2 = 0.8
Rating of capacitor Qc = kW(tan phi 1- tan phi 2 )
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / prakash g.r.
Calculation of Required Kvar
Initial or Present Power Factor =Qi,
Required Power Factor = Qd
KVAr= KW(TANQi-TANQd)
Qi=COS-1PFi = Initial Power Factor Angle
Qd=COS-1PFd = Final Power Factor Angle
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / ahatesham
at 0.5pf Apparent power is 10/0.5=20VA
reactive power = 17.321kVAR.
At 0.8pf
APPARENT POWER =10/0.8=12.5VA
Reactive power=7.5kVAR
So we need to provide (17.321-7.5)=9.821kVAR reactive power
through capacitor to bring of up 0.8 from 0.5.
So we need a capacitor rated for approximately 10kVAR to
achieve the target.
ANS= CAPACITOR RATING 9.821kVAR (approximately 10 kVAR)
| Is This Answer Correct ? | 2 Yes | 0 No |
Kvar = KW * [ tan (cos^-1* Current PF) - tan (cos^-1* Required PF)]
| Is This Answer Correct ? | 0 Yes | 0 No |
can HT cable or HT bare conductor used for LT line? is yes what would be the current rating?
how the capacitance is caluclated if the load is varying to keep the power factor constant(above0.95)
We have one Energy meter for Measuring the voltage,current,power,energy(KWH,KVARH,KVAH) & power factor.The problem is that the meter does not show whether the PF is lagging or leading.So i want to know that is there any way or calculation to find out that whether the PF sign (lagging or leading) depending upon the above mentioned parameters?
how the speed decreases of a generator in power station if load increases
can any one help me out by posting something related to rvnl interview for site engineer electrical.? what is the procedure? what kinda question they ask us? how long the interview goes? and any tips? and any thing you want to share?
How can we calculate D.C.Load current in terms of A.C. load current?
Impedance relay is directional relay or non directional relay?
how the earhing is done on ship and airplane.
is it possible to step down voltage of single phase from a three phase sysem? explain
What is the Load Capacity of Panther conductor (0.2) and dog conductor (0.1)
what is RMU ?
26 Answers MacLellan, Shalaka Infra Tech,
some times voltage does not built in small generators why ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)