If the load is 10Kw and power factor has to improve from 0.5
to 0.8,how can we select the capacitor rating
accordingly.Illustrate by showing formula?
Answers were Sorted based on User's Feedback
Answer / guest
at 0.5pf Apparent power is 10/0.5=20VA
reactive power = 17.321kVAR.
At 0.8pf
APPARENT POWER =10/0.8=12.5VA
Reactive power=7.5kVAR
So we need to provide (17.321-7.5)=9.821kVAR reactive power
through capacitor to bring of up 0.8 from 0.5.
So we need a capacitor rated for approximately 10kVAR to
achieve the target.
ANS= CAPACITOR RATING 9.821kVAR (approximately 10 kVAR)
Is This Answer Correct ? | 10 Yes | 2 No |
Answer / prasad damodar bhoir
kvar= kw (tan phi 1- tan phi 2)
cos phi 1= 0.5, phi 1= cos inverse 0.5= 60
cos phi 2= 0.8, phi 2= cos inverse 0.8= 36.86
kvar= 10 (tan60 - tan 36.86)= 10 (1.73-0.74)
kvar= 9.9
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / h salim
Load = 10 kW
cos phi 1 = 0.5
cos phi 2 = 0.8
Rating of capacitor Qc = kW(tan phi 1- tan phi 2 )
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / prakash g.r.
Calculation of Required Kvar
Initial or Present Power Factor =Qi,
Required Power Factor = Qd
KVAr= KW(TANQi-TANQd)
Qi=COS-1PFi = Initial Power Factor Angle
Qd=COS-1PFd = Final Power Factor Angle
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / ahatesham
at 0.5pf Apparent power is 10/0.5=20VA
reactive power = 17.321kVAR.
At 0.8pf
APPARENT POWER =10/0.8=12.5VA
Reactive power=7.5kVAR
So we need to provide (17.321-7.5)=9.821kVAR reactive power
through capacitor to bring of up 0.8 from 0.5.
So we need a capacitor rated for approximately 10kVAR to
achieve the target.
ANS= CAPACITOR RATING 9.821kVAR (approximately 10 kVAR)
Is This Answer Correct ? | 2 Yes | 0 No |
Kvar = KW * [ tan (cos^-1* Current PF) - tan (cos^-1* Required PF)]
Is This Answer Correct ? | 0 Yes | 0 No |
What is the effect on in Zone and out zone fault if Phase side CT is Vk/2<30 mA and Neutral side is CT is Vk/4<30 mA for Transformer REF protection
how hydrogen or helium is a cooling agent for alternator./ generator of big size.
In Power cable specification what is U0/U and Um.
what is difference between ELCB, RCBO & MCB
how to calculate the neautral earthing conductor size for a 500kva dg set.
how a single machine can act as both motor and generator? and give explanation interms of connections?
what is the difference between neutral and earth
How to synchoronize the generator (with gcb,GT) to grid????? ????? from Grid iam getting power (rated 400kv/20kv) through GT and its goes to UAT.,,ST.,, now my generator(rated 20kv ) ready.,, now iam closing my GCB.,, in GT iam suddenly giving 20kv on that Gt.,, what will happend
Difference between 3.5 core and 4 core
Why a Permanent Magnet Generator has higher frequency as compared to frequency of main alternator?
What is the exact minimum vale of voltage between an earth and netural which can damage or can do malfunction of the electronic equipments ? If this is mentioned in any book, pl.give reference.
0 Answers Bhushan Power Steel,
how can we connect a distance relay to CT core that is for backup protection or metering?