Why the power factor of the alternator in power plant is kept .8 lagging. Can't we maintain it at 1.
Answers were Sorted based on User's Feedback
Answer / sidharth
The pf is maintained at 0.8 because generator has to supply reactive power to the connected transmission line if pf is maintained at 1 then the distribution transformers would not be energized as it requires some reactive power for its core to produce magnetic flux.Also the due to line capacitance the receiving end voltages will get higher than the sending end voltages. For more reference consult reactive power control topic.
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / lokeshraj
We use the capacitor bank to maintain the power factor at .8 when it goes below this value, capacitor compensate the reactive power needed, and improves the power factor. Why don't we use this much value of capacitor that the pf becomes unity. Because if we use the capacitor at the load end and makes the pf unity the losses in the line will be decreased and the load capacity of the line will be increased.
Only in unloaded or lightly loaded condition the receiving end voltage of the line becomes higher than the sending end voltage.
| Is This Answer Correct ? | 1 Yes | 0 No |
For transmitting power with low value of ferrenty effect .power generating station pf should kept 0.85 -0.80
| Is This Answer Correct ? | 0 Yes | 0 No |
How CT is connected to measure current by changing plug setting , ratio is 300 - 150 / 5 A ?
1 Answers Ajanta Pharma, Bhel, Cosmo Films, Suzlon,
how oil in the MOCB was reduced compared with OCB? what are the features of the MOCB?
0 Answers Asahi, BARC, K-Electric,
I have 500A load (WHICH IS SEPARATE MDP PANEL),an MCC panel with 4000A Breaker.Already I have 2500A load.Can I connect this load directly to the Busbar since I have PROTECTION IN MY MDP Panel ?
Which do you think is the most significant cause of energy loss in a factory?
Pl. give me checklist for installation & commissioning of machine tool.
how we can find out the speed of fan without using any measuring instrument
why ac supply neutral should earth not in dc (-)
Why we used 690V in ACS 800 drives.Why dont use standard voltage like 415v or 1.1Kv
why two windings are using in single phase AC motor
list the advantages of RCCB over other circuit breakers?
What is the basic difference among Circuit breaker,Contractor and Isolator? Are they different names of same device/equipment?
How does frequency affect KVA rating of a transformer? If a 500 kva, 500 to 250 v, 60 hz t/f used in Canada is to be operated on 50 hz in Europe frequency then how will its KVA rating change? a-increase b-decrease c-remains same
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)