Can a 50-Hz designed transformer be used at 60-Hz system?
Is the same remains true, when a 60-Hz designed transformer
be used at 50-Hz system? Consider only frequency variation.
The voltage remains as rated value in all cases.
Justify the answer.
Answers were Sorted based on User's Feedback
Answer / iamdon
A 50-Hz designed transformer can be used at 60-Hz system
but a 60-Hz designed transformer cannot be utilized at 50-
Hz system.
Because in later case, the transformer windings(primary and
econdary)will draw approximately 20 % greater current than
the rated one.More current flowing will produce more
winding heating loss.The temperature of winding rises
(Beacuse cooling system was designed for rated current
which was lower as compared to present higher value of
current at low frequency operation)and it get burnt.
Author:arbelectbit@yahoo.com
Is This Answer Correct ? | 8 Yes | 3 No |
For a transformer the voltage is proportional to the product of flux and frequency.
case-I
Voltage = constant
Frequency = increased from 50 to 60Hz i.e. change by 120%
For Transformer:
Voltage = flux * frequency * K; k is a constant
so when frequency increases by 120% flux decreases to 83.3% Now;
Hysteresis loss = flux^2 * frequency^2 * T; T is constant
At 50 Hz
Hy. Loss@50 = flux^2 * Frequency^2 * T
At 60 Hz
Hy. Loss@60 = (.833flux)^2 * (1.2Frequency)^2 * T
On evaluation:
Hysteresis loss@50Hz = Hysteresis loss@50Hz
Eddy Current Loss
Eddy C. L. = flux^1.6 * f * C; C is a constant
Eddy@50 HZ = flux^1.6 * f * C
Eddy@60 Hz = (.833flux)^1.6 * 1.2F * C
On evaluation;
Eddy@60Hz = 0.895 * Eddy@50HZ
So it is seen that a 50HZ transformer when operated at at 60Hz has same hysteresis loss eddy current decreases. As the core loss decreases the transformer can be safely operated.
But if a 60Hz transformer is operated at 50Hz, then just the reverse of above the core loss i.e. eddy current loss will increase and hence the core loss will go high; hence not advisable to operate.
Is This Answer Correct ? | 0 Yes | 0 No |
how the capacitor work on dc?
whats happen if we disconnect the NGR of alternator in running condition?. Generally we observed that transformer netrul is directly grounded but alternator connected with NGR, then ground?
if the back emf eqution for dc motor EB=(QPNZ/60A) THEN what is the value of A for PMDC MOTOR OR how can dicide the value of "A"
Difference between KW & kVA
what you mean ct ratio? why use 400/5a,200/5a,150/5a ?
how to select overload-relay for perticular motor 1.for D.O.L. starter 2. for Star-delta starter ????
please send me jindal previous aptitude and technical question and answer.my email id is deep_raj@live.com
what is mean by kneepoint voltage? when it will happen? ( my doubt is, if CT secondary is open means ct get saturation or blas? what are factors are required for calculations? plz give currect anws:
1.4 What is meant by CT knee point voltage and how would you determine it
1.WHAT IS A SMART CAPABLE DB ( DISTRIBUTION BOX) ? 2. HOW TO DECIDE THE TYPE OF DB TO BE USED ( RECESSED/ PLUG TYPE/ SMART ETC ETC? 3. WHAT IS MILLENEUM BUS BAR USED IN DB? 4.DIFFERENTIATE MCCB AND MCB.
WHAT IS A BASIC DIFFERENCE BETWEEN THYRISTOR,TRIAC AND A DIAC.AND WHAT R THERE APPLICATIONS?
what is the difference between gsm and cdma??