I have running 4 generator in paralel.All generators
Voltages is same(470 V),KW also same (100 KW) but only No2
generator Amper is high than another generators.
DG No:1,3,4 470V,100KW, 150 A
DG No:2 470V,100KW,400 A
Answers were Sorted based on User's Feedback
Answer / ruslan
Yes My friend it is possible.All meters are in good
condition.I also surprised.
| Is This Answer Correct ? | 3 Yes | 0 No |
This is caused by kvar. If the excitation is higher (field
voltage) it will take more kvar. This will only be shown by
a current not load. The KW will remain the same.
Reduce the excitation (voltage setting on the AVR) on No 2
generator until it is reading the same current as the other
3 generators.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / afzaal
what?how could that be possible?with the same power ,the same voltage u get more amps....please check your instruments first..there must be some faulty meters..if not then i am too interested in knowing the answer of it
| Is This Answer Correct ? | 1 Yes | 3 No |
why in scott connection of transformers, main transformer is tapped at 50% and teaser transformer at 86.6%?
5 Answers Bhel, Bosch, College School Exams Tests, Wipro,
Alternator couple to diesel engine why, Alternator couple to ac service motor with gear drive for 1500 rpm possible (yes or no) aim to low input power supply give to motor then high output power taken for alternator Please answer this question
A 15 kw squirrel cage motor having a maximum efficiency of 90% on a continuous full load has temperature rise of 42 degrees celcius after 30 min and 52 degrees celcius after 1 hr under the above operation conditions. a) calculate its final steady state temperature rise on continuous load and the heating time constatnt. b) if the motor is operated on a short load for 9 min estimate its temperature rise. c) calculate the maximum overload that can be applied on a short, 9 min rating so that the temperature rise is the same as the final steady state temperature rise on continuous load.
Can Induction motor run at over rated speed? ( 15oo rpm is rated speed for 50HZ. is it possible to ride 3000 RPM with same motor with the help of VVVFD for continues ride of 100HZ)
Dir sir we have 750 kva Caterpillar dg set we are fas on different problem we start dg set ofter 1 mint apply load around 500a dg was run one or 3 mint after 3 mints dg was shutdown automatic how to face tis problem
How can we convert dc to equivalent ac??
What is potientometer.How it is useful in a sychronoscope.
Which type of a.c motor is used in the fan (ceiling fan, exhaust fan, pedestal fan, bracket fan etc) which are find in the houses ?
WHY IL=IPH IN STAR AND WHY IPH=IL/1.732 IN DELTA? WHAT IS REASON BEHIND IT?
what is on line transformer and off line transformer.
Write the force balance equation of m ideal mass element.
Why pmg used in electrical generators for excitation.is there any other method without pmg ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)