I have running 4 generator in paralel.All generators
Voltages is same(470 V),KW also same (100 KW) but only No2
generator Amper is high than another generators.
DG No:1,3,4 470V,100KW, 150 A
DG No:2 470V,100KW,400 A
Answers were Sorted based on User's Feedback
Answer / ruslan
Yes My friend it is possible.All meters are in good
condition.I also surprised.
Is This Answer Correct ? | 3 Yes | 0 No |
This is caused by kvar. If the excitation is higher (field
voltage) it will take more kvar. This will only be shown by
a current not load. The KW will remain the same.
Reduce the excitation (voltage setting on the AVR) on No 2
generator until it is reading the same current as the other
3 generators.
Is This Answer Correct ? | 1 Yes | 1 No |
Answer / afzaal
what?how could that be possible?with the same power ,the same voltage u get more amps....please check your instruments first..there must be some faulty meters..if not then i am too interested in knowing the answer of it
Is This Answer Correct ? | 1 Yes | 3 No |
why did the BDV test in transformer?
2 Answers Jindal Steel and Power,
How Many safety of Air circuit breaker
What is means by MacAdam Ellipse?
Name a govt approved university which have 100% online engineering course.
Can I use measuring current transformers in protection purposes?
which type sylbuse involved
are you hear the meaning of burden , excat meaning of burden in only one word
If Ac supply is given to the DC motor then what will happen? clear explanation
why CERAMIC material is used in insulators??
Why the cost of CT increases with the decreasing of its CT Ratio (Technical Reason)?
what is the differnce between high impedance relay and low impedance relay
WHAT IS PRINCIPLE OF TRANSFORMER