there is a # KVA Transformer of 11 KV/440V, in simple(not use formuia) how can you calculate it's HT & LT side current.
Answers were Sorted based on User's Feedback
Answer / guest
Dear P.Kalivada 100KVA transformers total power (3 phase) is 100KUA one phase give 33KVA, Phase voltag is 11/1.732 = 6351 volt therefore current is 33000/6351=5.1 amp (at unit pf). You can see a name plate of 100KUA 11KV/433v tranrsformer it is written 5 amp as HT Current and 133 amp as LT side current you can verify any tranformer whose primary voltage is 11KV it's current is approximately to #/20 and secondary side of 433V it's current is approxhmately to # +#/3 ( # is how much KVA)
| Is This Answer Correct ? | 17 Yes | 5 No |
Answer / guest
HT side current = #/20 LT side current =#+#/3 ie 100KVA 11KV/440V transformer it's HT side current = 100/20=5 amps LT side current=100+100/3=133 amps. this is approximatelly figure(answer), Line man of Power Distribution Company fallow this method .
| Is This Answer Correct ? | 8 Yes | 6 No |
Answer / sunit
this is simple .. assume a 100kva tr, ok
then p= vi ( power = voltage x current)
1.lets see for HT side
p( kva)= root 3 ( for 3 phase)x voltagex current
=> kva = root3xvxI
=> 100kva=1.732x11kvxI
=> I= 5.25amp/phase
2. similarly in secondary side means LT side
=> 100kva=1.732x440xI
=> I= 144amp/phase
| Is This Answer Correct ? | 8 Yes | 6 No |
Answer / zaman
5KW capacity motor stare connection 410 volt pf 1 current 7.5 amp how mouch current carry of delta connection
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / prashant kalivada
KVA = KV x A
= voltage in KV x current in ampere
So, A = KVA / KV at HT side
therefore if KVA is 100 and KV is 11 then
A= 100 / 11
= 9.09 Amps at HT side
and for LT
A = KVA / (V/1000)
= 100 / (440/1000)
= 100 / 0.440
= 227.27 for LT side
| Is This Answer Correct ? | 6 Yes | 10 No |
dielectric strength of vacuum is greater than SF6 but for 132Kv uses sf6 breaker & for 33kV uses vaccum breaker why such a contradiction?
2 Answers MSETCL Maharashtra State Electricity Transmission Co Ltd,
what is the calculation involved to design the heater to heat 10KL of water in temperature control unit?
What is ELR, and where it is used ?
i am having a 3 phase 12.5HP motor,that is connected in Star/delta.Without any Trip that motor stopped suddenly why?
1. When do you use a VFD motor? 2. If the ceiling fan is on slow speed, does it consume less electricity? 3. If we want the fan to consume less electricity at low speed, what do we have to do? 4. What does “battery of 180 AMP HOUR” mean to you? 5. What does “battery of 180 AMP HOUR” mean to you? 6. If you don’t have coal, salt and copper, then how would you earth your connection temporarily at a camp site.?
6 Answers Asian Power, Bhel, Focus, Focus Energy, L&T,
Does the Impedance of the source affects the THD
We have a 62.5 KVA DG with Leyland engine and kirloskar slipring alternator. We have earthed the neutral, and another earthing for the dg body. is it necessary to isolate the dg foundation with rubber pads?
What is surge impedence and surge loading....???
what is main purpose of ignator in halogen lamps.how to identify the failer of ignator in circuit
what is the difference b/w circuit breakers and relays?
how to reduce power loss when the tranmission under long distance?
what is the wattage of 'zero watt' bulb?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)