there is a # KVA Transformer of 11 KV/440V, in simple(not use formuia) how can you calculate it's HT & LT side current.
Answer Posted / guest
HT side current = #/20 LT side current =#+#/3 ie 100KVA 11KV/440V transformer it's HT side current = 100/20=5 amps LT side current=100+100/3=133 amps. this is approximatelly figure(answer), Line man of Power Distribution Company fallow this method .
| Is This Answer Correct ? | 8 Yes | 6 No |
Post New Answer View All Answers
what is the purpose of shading ring or shading coil in electrical equipments.
What is I to C?
Is it good to short Neutral and Ground in the PLC or DCS main Power supply. Pls give YES or NO with reasons...? Simarpreet
how to select diiferent power transformers of same capacity on no load loss and full load loss by economical point of view.?
How each of the following losses occur in d.c machines (i) copper (2)core (3) windage (4)friction please help me
what is plunger and what's the use of it in motor alignment?
What is the meaning of loop in transformer
why single CT used in DOL starter power circuit?
What is Instantaneous Earth fault relay,how will work
What happens if the series current double?
How many energy meters can be connected on a 15VA Voltage transformer. please send a calculation sheet.
how synchronous condenser is used in place of synchronous generator with out negotiating IEEE standards? Can i use 3 generators as synchronous generators and 2 generators as a synchronous condensers in an IEEE 14 bus system with out disturbing the standards?
In Designing the rating & accessories of a MCCB how to choose the type of releases..means what is the basis for selecting, thermal magnetic, electromagnetic & microprocessr based releases
HOW TO CALCULATE HV CABLE SIZING?
What is MSL designation of a motor and same may be provided in details.