In a 3Ph induction motor(old) 6 wires came out from terminal
& not mentioned u1,v1,w1,u2,v2 & w2. how can find out the
terminals? how can connect to star delta starter??
Answer Posted / raovasuki17
first of all you have to use multimeter to identify the
coil teminals. segregate it in two lines as 2 x 3 . ie top
3 terminals and bottom 3 terminals.
Next take a Small DC power supply with 3 volt and a
milliampere meter( DC ). connect this voltage to one of the
coils with milliampere meter in series( Milliampere meter
should be of center zero type ) close the supply voltage to
the coil with make and break it immediately. observe the
deflection whether it is on forward side or reverse side.
and mark one terminal for whcih +ve suplly is connected as
Start and the other ( _ ve )end as Finish. do this
process for other two coils also. once you know the top 3
start points and finish points of the coil. you are almost
there. now you short ckt all finish ends. you are left
with 3 start terminals. ie your STAR connection.
For Delta connection connect finish end of the first coil
to start end of the second coil, finish end of second coil
to start end of third coil and finish end of 3third coil
to start end of first coil. now you have theree junctions.
now your connection is in Delta mode.
| Is This Answer Correct ? | 17 Yes | 2 No |
Post New Answer View All Answers
Why control of DC motor is simpler?
how the characterstics of control valve being done
Name one of major transformer company in KSA ?
Which type of air compressor is used now a days in the market. Keeping in mind of energy efficiency and maintenance points. Relevant documents may also be sent on mentioned email ids.
How to calculate cable size in HT AND LT
why we take movement of rotor always in counter-clockwise direction in 3-phase induction motors?
How to measure the Harmonic Distortion of UPS ie THD?
Vaccum circuit breaker
What is the maximum number of swithes that can be connected in series up to down stream point in an LV Distribution system?
what is the difference b/w ATS and HTS?
what is the difference between elcb and rccb ?
when will be the iocl interview results i faced interview on 8th september 2008 iam from electrical branch i faced interview for the post of electrical engineer??????????????????????//
how to calulate short circuit current for the following: 1.cable connecting 11KV of 22KV/11KV transformer to 11Kv of 11KV/415V transformer 2.what cable size should i use.
What are the site acceptance tests for power cables, DG Sets, LT panels & 30kVA UPS ?
Both generator parallel condition shared load equally but one genrator taking ampere more than the other what are all the causes to make like this