Answer / sachin
Power factor Basics
In all industrial electrical distribution systems, the
major loads are resistive and inductive.
Resistive loads are incandescent lighting and resistance
heating. In case of pure resistive loads,
the voltage (V), current (I), resistance (R) relations are
linearly related, i.e.
V = I x R and Power (kW) = V x I
Typical inductive loads are A.C. Motors, induction
furnaces, transformers and ballast-type
lighting. Inductive loads require two kinds of power: a)
active (or working) power to perform
the work and b) reactive power to create and maintain
electro-magnetic fields.
Active power is measured in kW (Kilo Watts). Reactive power
is measured in kVAr (Kilo
Volt-Amperes Reactive).
The vector sum of the active power and reactive power make
up the total (or apparent)
power used. This is the power generated by the SEBs for the
user to perform a given amount of
work. Total Power is measured in kVA (Kilo Volts-Amperes)
The active power (shaft power required or true power
required) in kW and the reactive
power required (kVAr) are 90° apart vectorically in a pure
inductive circuit i.e., reactive power
kVAr lagging the active kW. The vector sum of the two is
called the apparent power or kVA, as
illustrated above and the kVA reflects the actual
electrical load on distribution system.
The ratio of kW to kVA is called the power factor, which is
always less than or equal to
unity. Theoretically, when electric utilities supply power,
if all loads have unity power factor,
maximum power can be transferred for the same distribution
system capacity. However, as the
loads are inductive in nature, with the power factor
ranging from 0.2 to 0.9, the electrical dis distribution
network is stressed for capacity at low power factors. So
COS PHI= KW/KVA
Is This Answer Correct ? | 6 Yes | 0 No |
Answer / balu
power factor is the ratio between active power and apparent
power. apparent power = active power + reactive power.
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / mubeen
a angle between voltage and current on running load is
called power factor.If its value is increase performance of
motor or equipment will improve.
Is This Answer Correct ? | 0 Yes | 3 No |
How many 2 ton window A/c can runs on a 125 KVA generator?
how we are desining 63.5 ohm resistor for NGR of alternator?
difference between analog pressure gauge & digital pressure gauge?
why 3 phase motors are preferable over single phase motors ?
why voltage coil in wattmeter called as pressure coil why the pressure term is used in wattmeter?
what is the necessity of neutral in 3 phase system?
what is REF relay?
WHAT IS IM (INDEX OF MOUNTING )IN MOTORS
how to find the multiplication factor for digital energy meter and analog energy meter
why the neutral point is zero in star connection?
when we increase load , current drawn from source also increases why ?
what is meant by lagging & leading current