Can 2 nos. of 1 ton split ac be used through a 20 am supply
meter?
Answers were Sorted based on User's Feedback
Answer / gskasherwal
yes 1ton split ac having 1.2 kw power so 1.2*2=2.4 kw which can be used on single phase meter.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / s.ghosh
The answer is "Yes" for steady state current, but "No" for
starting current. You can use the 20A capacity line for 2
nos. 1T AC, but you have to ensure that at no instance, both
the ACs are switched on simultaneously.
Is This Answer Correct ? | 0 Yes | 1 No |
Difference between shunt, PMG and AREP excitation. Which is the most reliable between PMG and AREP.
WHAT IS THE COMPLETE DEFINATION OF POWER FACTOR?HOW IT CAN BE IMPROVED?AND WHAT IS CAPACITIVE LOD AND INDUCTIVE LOADS
what is the significance of KV & MVA rating of the transformer and how they are related.
What do you mean by ratio correction factor of instrument transformer?
what is diff btw electric,magnetic & eletromagnetic field
Is a induction motor rotate by back emf ? If not , then how it is rotate ?
how the BDV of the oil will be checked using moterised controled HV SET?
how can check the resistance of battery contact?
One of our gas turbine generator unit "1st stage rotor ground fault" alarm was occured several times. we tried to measure some voltage vulue ground fault protection relay (UNS3020a made by ABB and we measured the value of: Ground: 0.9VDC 5V: 5.8VDC 24V: 23VDC u+: 300 – 350mVAC Rf1: 17.5mVAC Rf2: 17.6mVAC The unit still running and the alarm was reset. As of 6pm yesterday and unitl now no alarm happened again. I our protection relay was defective?
What will happen if the d.c. Shunt motor opened accidentally running on no-load has its shunt field winding?
I have a 3 phase 600 volt prim. feed and a 120/208 sec. Isolateing tranformer .We are using this system for safety against shock . What is the proper grounding ?? Does the common on sec. get earth ground ???
Two electric lamps 40 W, 220 V each are connected in series across 220 V. What is the power consumed by the connection?