Can 2 nos. of 1 ton split ac be used through a 20 am supply
meter?

Answers were Sorted based on User's Feedback



Can 2 nos. of 1 ton split ac be used through a 20 am supply meter?..

Answer / s.sarkar

No,for two AC minimum 30A meter required.

Is This Answer Correct ?    0 Yes 0 No

Can 2 nos. of 1 ton split ac be used through a 20 am supply meter?..

Answer / gskasherwal

yes 1ton split ac having 1.2 kw power so 1.2*2=2.4 kw which can be used on single phase meter.

Is This Answer Correct ?    0 Yes 0 No

Can 2 nos. of 1 ton split ac be used through a 20 am supply meter?..

Answer / s.ghosh

The answer is "Yes" for steady state current, but "No" for
starting current. You can use the 20A capacity line for 2
nos. 1T AC, but you have to ensure that at no instance, both
the ACs are switched on simultaneously.

Is This Answer Correct ?    0 Yes 1 No

Post New Answer

More Electrical Engineering Interview Questions

Difference between shunt, PMG and AREP excitation. Which is the most reliable between PMG and AREP.

0 Answers   ABB,


WHAT IS THE COMPLETE DEFINATION OF POWER FACTOR?HOW IT CAN BE IMPROVED?AND WHAT IS CAPACITIVE LOD AND INDUCTIVE LOADS

2 Answers  


what is the significance of KV & MVA rating of the transformer and how they are related.

8 Answers  


What do you mean by ratio correction factor of instrument transformer?

0 Answers  


what is diff btw electric,magnetic & eletromagnetic field

0 Answers   Senthil,






Is a induction motor rotate by back emf ? If not , then how it is rotate ?

1 Answers  


how the BDV of the oil will be checked using moterised controled HV SET?

1 Answers  


how can check the resistance of battery contact?

0 Answers   Cipla,


One of our gas turbine generator unit "1st stage rotor ground fault" alarm was occured several times. we tried to measure some voltage vulue ground fault protection relay (UNS3020a made by ABB and we measured the value of: Ground: 0.9VDC 5V: 5.8VDC 24V: 23VDC u+: 300 – 350mVAC Rf1: 17.5mVAC Rf2: 17.6mVAC The unit still running and the alarm was reset. As of 6pm yesterday and unitl now no alarm happened again. I our protection relay was defective?

1 Answers  


What will happen if the d.c. Shunt motor opened accidentally running on no-load has its shunt field winding?

0 Answers  


I have a 3 phase 600 volt prim. feed and a 120/208 sec. Isolateing tranformer .We are using this system for safety against shock . What is the proper grounding ?? Does the common on sec. get earth ground ???

1 Answers  


Two electric lamps 40 W, 220 V each are connected in series across 220 V. What is the power consumed by the connection?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)