Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


Why hunting will occour in control valve?

Answers were Sorted based on User's Feedback



Why hunting will occour in control valve?..

Answer / s vedpathak

Control valve is used in close loop control system.If it is
hunting , then to troublshoot first put loop for few sec in
manual mode, still if v/v is hunting then it is field
problem i.e v/v or I/P converter problem.

If it is not hunting in manual mode, then the problem can
be either the loop process variable(PV) is hunting or if PV
is ok, either the load/process is varied or loop needs
tuning.

Is This Answer Correct ?    57 Yes 1 No

Why hunting will occour in control valve?..

Answer / kumar

1)I/P PROBLEM
2)INSTRUMENT AIR LEAK(Signal)
4)FLOW DISCHARGE FROM THE PUMP MAY FLUCTUATING.

Is This Answer Correct ?    15 Yes 2 No

Why hunting will occour in control valve?..

Answer / mahesh kumar

Hunting Occur in theControl Valves due to inproper tuning
of PID loop, to remove thr hunting & for smooth operation
Tune the PID loop by adjusting the Gains

Is This Answer Correct ?    17 Yes 7 No

Why hunting will occour in control valve?..

Answer / sam.r

An undesirable oscillation of appreciable magnitude,
prolonged after external stimuli disappear. hunting is the
evidence of operation at or near the stability limit.

in control valves is caused by the oscillation in the
loading pressure to the actuator caused by the instability
in the control system or the valve positioner .

Is This Answer Correct ?    5 Yes 2 No

Why hunting will occour in control valve?..

Answer / sujitkumarnaik@indiatimes

if there is haunting in c/v that means there is disturbance
in i/p signal & o/p signal or feed back.so firstly calibate
it n observe.if still same prob. coming,adjust the pid tunning.

Is This Answer Correct ?    4 Yes 3 No

Why hunting will occour in control valve?..

Answer / mostafa abo el-kasem

Several reasons can cause valve hunting; it can be from signal or from hard ware
To define:
1- Check controller o/p is stable while valve “you can put it in manual mode” is hunting or not (if not stable then it could be from the configuration or from PV change, you can check transmitter/damping/configuration,)
2- If signal is ok ,then it will be hardware problem from
a. Feedback arm not fixed
b. I/P problem
c. Diaphragm damage
d. Flow irregularities
e. Positioner tuning

Is This Answer Correct ?    1 Yes 0 No

Post New Answer

More Instrumentation Interview Questions

Why grounding is necessary? Give example with diagram.

0 Answers   Bright Point, DS Group,


how many types of sensor in instrumentation

3 Answers   SRACO,


where can we use viberation transmitter,and how can we control viberation?

1 Answers   Maden,


What is the Difference between PE,IE and ISE

2 Answers  


How to convert Differential pressure to flow in TPH

0 Answers   Chettinad, ELCO,


What are Sinking and Sourcing IO Cards

2 Answers  


relation between flow and differential pressure.

7 Answers   ABB,


Why we are using thrust bearing at turbine side?

3 Answers   Edac,


WHEN BOTH WIRES OF THERMOCOUPLE R SHORTED WHAT IS THE OUTPUT THE TEMP ARE 0,30,250,320

13 Answers  


how ranges is decided for drum level or dearator level,in my pplant i have seen for boiler drum range is -1000 to 1000mmwc, while for dearator -2000 to 0 mmwc ,why they decided to take this range ?

2 Answers  


please send the drdo exam paper

0 Answers   DRDO,


Can I put my meter across an RTD to check it safely witout tripping the equipment when it is connected to an monitoring device eg.RTD module or IQ 1000

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)