our company have 750 kva oil transformer.still we have
facing a problem that is when voltage is 11.5 kv coming
from HT side then LT-side voltage is 420v or above at tape
1.please give me best solution to decrease the voltage
Answers were Sorted based on User's Feedback
Answer / sudhakar lanka
my friend, you r looking for reduce the output voltage from 420 volts,
case1: try to keep the primary tap position on maximum voltage
for example ur receiving 11.5kv , if in your transformer there is a tap voltage which is more than these value i.e 11.6kv or else apply 11.5kv on that tap position.
same as above u can try on secondary side also
case2: if u have done all the these exercise, then when u connected to load on transformer there will be voltage drop
check at that time may be ur required voltage i.e rated voltage on motor or machine when it is running on load
other wise u can check with grid supply or substation to get required voltage
Is This Answer Correct ? | 4 Yes | 0 No |
Both the voltages are 5 % higher than the normal voltages ,that means tap position is for normal primary voltage . Check the name plate details
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / k.prakashchandra
From the data furnished by you ,it appears that Tap No.1 is
the normal position as there is 5% rise in both primary and
sec voltages, for 11KV/400V Tr
Is This Answer Correct ? | 0 Yes | 1 No |
explain Uninterrupted power supply detailed electronical operation with circuit diagram
. Is there a simple method to measure the horsepower of a small motor (1-3 hp) for a non-technical person
How many types of fault occur in a 3-phase power system?
can we connect transformer with star conected secondary to delta connected primary in series?
What is the lower limit of break-down voltage of converter transformer.
Can any one provide the inspection procedure of MIMIC for VFD panel? Details: If someone wants to have a mimic in the VFD panel what are inputs considered for the mimic(like on,off,trip) whether we are able to add speed variation in the mimic(if so how can we get) and what are the parameters to be checked in the MIMIC during inspection?
what is the function of supervison relay?Draw its wiring diagram.
2 Answers IBM, R.R. ISPAT LIMITED,
In Single Phase AC Supply,If Voltage between Phase and Neutral is 230V means what will be the Voltage between Phase and Earth?
Why the voltage n frequency of the incoming generator is kept slightly higher than d grid voltage n frequency while synchronization ?
What is CCTV System???Applications........
16 Answers Emerson, Honeywell, Joyalukkas,
Why Parallel operation of two Transformer are Required?
What is it mean Transformer 100/133MVA Power Transformer, significance of 100/133 MVA and 230/115KV please