our company have 750 kva oil transformer.still we have
facing a problem that is when voltage is 11.5 kv coming
from HT side then LT-side voltage is 420v or above at tape
1.please give me best solution to decrease the voltage
Answers were Sorted based on User's Feedback
Answer / sudhakar lanka
my friend, you r looking for reduce the output voltage from 420 volts,
case1: try to keep the primary tap position on maximum voltage
for example ur receiving 11.5kv , if in your transformer there is a tap voltage which is more than these value i.e 11.6kv or else apply 11.5kv on that tap position.
same as above u can try on secondary side also
case2: if u have done all the these exercise, then when u connected to load on transformer there will be voltage drop
check at that time may be ur required voltage i.e rated voltage on motor or machine when it is running on load
other wise u can check with grid supply or substation to get required voltage
| Is This Answer Correct ? | 4 Yes | 0 No |
Both the voltages are 5 % higher than the normal voltages ,that means tap position is for normal primary voltage . Check the name plate details
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / k.prakashchandra
From the data furnished by you ,it appears that Tap No.1 is
the normal position as there is 5% rise in both primary and
sec voltages, for 11KV/400V Tr
| Is This Answer Correct ? | 0 Yes | 1 No |
How i can calculate current of cable according to ares?
what will hapen if secodery circuit is open of current transformer WHy neutral to ground trips when neutral touches the ground
Which type of power plant is more easier to produce electrical power at economical condition?
How can calculate the efficency of the rectifier. input 240V AC, current 5 amps,P.F 0.98, Output is 54 V DC,62.6 A.
if field winding of synchronous generator are shorted on each other will it start or burn or run for short time like induction motor
What will happen if the armature resistance is in minimum position and the field resistance is in maximum position while starting the motor
what is LOS(line of sight)?
how to reduce shorting current in a slipring induction motor
how to work exciter in 10 MW alternator?
Dg daily a check duration
HOW CAN WE DECIDE THE SUPPLY VOLTAGE FOR MOTOR ACCORDING TO ITS RATING(IF ANYONE KNOWS GIVE IT WITH EXAMPLE AND ITS CALCULATIONS)
how to give earthing in ships?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)