HOW DOES SPECIFIC GRAVITY AFFECT LEVEL MEASUREMENT.
Answers were Sorted based on User's Feedback
Answer / salamah alnazzal
Well, Level is represented as function of pressure (P) and
pressure is function of height and S.G as basic level
measurement. So, The Formula for Pressure is P=S.G*H.
However, Each liquid has it's won unique S.G such as Oil
vs. Water, 0.6 and 1 Respectively.
Based on above, we do see clear impact to level measurement
when S.G changed. SG has direct impact to level measurement
in case of Differential pressure measurement type is used
or displacer type. Other type of level measurement will
have no impact such as Rader , Capacitance etc.
has no impact to level measurments.
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / akkkkki
when measuring pressure using pressure gauge formula for
pressure is given as
p=rou*h*specific gravity.
here h is the measure of level height
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / mithilesh kumar
Level measurement formula is
(§.g.h) roh.g.h.
specific gravity is varies.
It's depends upon process parameter.
For eg. Steam water gravity is different.
| Is This Answer Correct ? | 1 Yes | 4 No |
what is RPI and NUT in controlnet networx. what happen if we are increase the NUT of controlnet networx?
how many parts of valve positioner?
What is upsampling and downsampling?
What unit is used for measuring comp. outlet flow. it is CFM, M3/hr or NM3/hr. ?
Calculate the maximum pressure drop that can be allowed to occur across a control valve, so that we can prevent cavitation / flashing from occurring. Use the following formula: Δ P allow = Km (P1 – PvapourA) where, Δ P allow - the maximum allowable differential pressure for sizing purposes, or terminal pressure drop; Km- the valve recovery coefficient from the manufacturer’s catalogue; P1 - absolute inlet fluid pressure; PvapourA - absolute fluid vapour pressure at the inlet temperature; Use Atmospheric pressure = 101.3 kPa, P1 = 1200 kPa(g), PvapourA = 4 kPa, KM = 0.72
How can I zero check of wet leg type DP Tx ?
What are the type of bonnets in the control valves?
deference between DCS and PLC including date processing and architacture.
how can be calibrate flow indication transmitter (rosemount) it shows excess milli amps nearly about 24 ma on full scale, but its scale was set on 20ma on full scale..???how can be simiulate..???
LADDER LOGIC Can any body state Logic on following condition Instructions to use 1-XIC 2-XIO 3-Output ONLY Program Push 1st button On - 1st lamp should On Then Push 1st button Off - 1st Lamp Should remain on Push 2nd button On - 1st lamp should Off and 2nd lamp should On Then Push 2nd button Off - 2nd Lamp Should remain on.
May I have a brief note above the voltage barriers? Whats is the purpose? Please mail me if you've operational details, mail id: rajkumar.diice@gmail.com
What is the use of +/- 20ma in analog measurement,and which instrument gives +/-20ma output
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)