Is it possible that Generator trip but Turbine not trip.Give
explanation.
Answer / k.prakashchandra
It happens if turbine trip circuit is not connected to
master trip relay.If the generator trips alone on load , the
turbine may trip due to over speed.
| Is This Answer Correct ? | 3 Yes | 1 No |
we use capister for power factor. when we use capaciter in dg circuit than defect dg. can we use capaciter bank for dg circuit
what does hapen if suddently frequency doubled
What is the function of a neutral reactor.
what is the working principle of ceiling fan and table fan?
10 Answers ABC, Tata Steel Limited,
am commissioning the trafo without connecting the neutral therefore unbalance will occur what is the alternative solution for this?
which of the following elements is not present in stainless steel
Why we have short circuit the secondary of the transformer
What is the criteria for selecting the voltage classes of an AC Induction Motor.The KW rating above/below which ht/lt selection is made may be provided in details.
its Kva and Kv are same?
Why there are semi conductor layers on conductor and XLPE insulation of HT cables
How to calculate the time setting for star connection in star delta starter? For example 10KW 3PH Induction motor.
0 Answers Taj Group, Tata Steel Limited,
which stabilizer is better ? AVR, Servo Stabilizer, Static stabilizer etc & why explain it
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)