how to calculate the knee point voltage of current
transformer?
Answers were Sorted based on User's Feedback
CT resistance = 1.8ohm,
Lead resistance = 4.0 ohm,
Starting current = 195*5/200 = 4.875 Amp
Starting voltage = 4.87(1.8+4)= 28.275 = 28.3 volts
This is to be set to 30Volt,
But please remember that knee voltage should be 60 volt
minimum.
For anymore clarification you can mail me to :-
manisand1@hotmail.com
Is This Answer Correct ? | 1 Yes | 1 No |
Answer / puneet prashar
Knee Voltage=2X Earth Fault current(RCT + RW)/CT
Trasformation ratio
Where
RCT= CT impedeance as per manufacture1.02
RW = Wire resistance as per manufactre
say.oo32/metre then RW= 2X 200mtr X .0032
CT transformation ratio= 4000/1=4000
4000/5=800
VKnee= 2X58000(1.02+1.28)/4000 or 800 depending upon ct used
Vknee= 66.7v
Vknee> relay stability Voltage
Relay stability voltage formula will be given by relay
manufacturer as every relar manufacturer has their own formulas
Is This Answer Correct ? | 0 Yes | 0 No |
what would u consider to be the basic purchase order information you would need to proceed with a cable inspection assignment?
Anybody know how schematic diagram for reverse power relay? RPR for generator protection
can we keep open the secondary of current transformer?
what is the resistance value of earthing pit and why they are connected?
how harmonics are generated due to nonlinear load & how harmonic filters work?
what is the range of thermal overload and over current. Answer should be in percentage of current.
I have 4 DG set with 1500KVA rating. system breakers are 11KV & alternator are 415 Volts. Between alternator & breaker one stepup transformer used. i want to Know what is max. resistance for body earthing & 415 & 11KV V Neuteal earthing. my fault current is 14 times for 2 sec.
what is the difference single phase and 3phase starter
How much CTs are required to measure th curent in DOL starting of motor?PLs explain.
What safety followup during kWh meter isolation
1.Is there any difference between terminologies,HT-HV <- LV? 2.What is the highest transmission voltage level in india?
why voltage coil in wattmeter called as pressure coil why the pressure term is used in wattmeter?