how to calculate the knee point voltage of current
transformer?
Answers were Sorted based on User's Feedback
CT resistance = 1.8ohm,
Lead resistance = 4.0 ohm,
Starting current = 195*5/200 = 4.875 Amp
Starting voltage = 4.87(1.8+4)= 28.275 = 28.3 volts
This is to be set to 30Volt,
But please remember that knee voltage should be 60 volt
minimum.
For anymore clarification you can mail me to :-
manisand1@hotmail.com
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / puneet prashar
Knee Voltage=2X Earth Fault current(RCT + RW)/CT
Trasformation ratio
Where
RCT= CT impedeance as per manufacture1.02
RW = Wire resistance as per manufactre
say.oo32/metre then RW= 2X 200mtr X .0032
CT transformation ratio= 4000/1=4000
4000/5=800
VKnee= 2X58000(1.02+1.28)/4000 or 800 depending upon ct used
Vknee= 66.7v
Vknee> relay stability Voltage
Relay stability voltage formula will be given by relay
manufacturer as every relar manufacturer has their own formulas
| Is This Answer Correct ? | 0 Yes | 0 No |
WHAT ARE THE FACTORS REQUIRED FOR SELECTION OF TRANSFORMER RATING?
13 Answers Tech Mahindra, Technip,
how to interlock 2 incomer,1 buscoupler MCCB,like we interlock an ACB... pls answer this question and if possible send me the ckt diagram..
Dear all,recently in our plant we installed a conveyor for this the motor ratings are 5 hp and Amps 7.39.Due to on urgent starting of conveyor we fix the DOL starter with range of 9-15 amps.give me suggestion regarding on this issue
WHAT IS DIFFERENCE BETWEEN CAPACITOR AND CAPACITANCE?
what is the size of cable for 15kw motor and 85 meter cable length using with vfd
How to convert farad to kvar. both are the unit of capacitor.
5 Answers College School Exams Tests, UltraTech, Vikram Ispat Industries,
what is the difference between Ith & Iu rating in MCCB. Particularly on SACE ABB Circuit Breaker?
why do we connect droop ct{in gensets}in y_phase only
what s a servo motor? how to control the servo motor? and its application, purpose of using?
WHAT IS THE FUNCTION OF PULSE TRANSFORMER IN DC DRIVE
Why should The rating of 11 kV DO Fuse is in mulyiple of hundred(200 Amp. 40 Amp, etc) Ampere wheareses the its fuse elemnt has rating in just few Amp (< 12 Amp)? ( Is it jusy beacuse of factor of safty).
sir, i want to know the calculation for find rated current for cable sizes.(both copper & aluminium) with examole. please sir for example: 35sq.mm al.cable is withstands for how many amps? is suitable for 45kw motor?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)