how to calculate the knee point voltage of current
transformer?
Answer Posted / manisand1
CT resistance = 1.8ohm,
Lead resistance = 4.0 ohm,
Starting current = 195*5/200 = 4.875 Amp
Starting voltage = 4.87(1.8+4)= 28.275 = 28.3 volts
This is to be set to 30Volt,
But please remember that knee voltage should be 60 volt
minimum.
For anymore clarification you can mail me to :-
manisand1@hotmail.com
| Is This Answer Correct ? | 1 Yes | 1 No |
Post New Answer View All Answers
What is resistance of 50meters, 16sq.mm, single core copper cable?
For high frequency application we use which transformer?
What is the basic principal, by which DC voltage level is increased more than the supplied AC voltage during conversion. As upto AC level it is contorrled by firing anlge but after maximum level how is it possible.Please clear picture. OR we have to supply the higher level AC?
what is die electric strnth of transformer ?
What is difference between Harmonic and Non harmonic Capacitor Bank?
what is size of 3phase 4wire cable to be used for 11 ton ductable A.C and how to calculate cable size for different load
What is critical disruptive voltage?
What is the power requirement of tamil nadu for one month?
What are the effects of electrical faults?
How to calculate the electrical load for a standard telecom BTS shelter and choose the DG set capacity for the same load?
can i connect the two phases of scott connected transformer,if not why?
Define availability (operational)?
What is minimum permicible value of leackage current for LT Panle when applying voltage up to 3 KV for 5 Minuits?
A car's starter motor draws a current of 100 A at 12,0 V when starting the engine. The mechanical power required to turn the engine is 960 W. At what rate is energy from the battery converted to non-mechanical forms of energy?
we have 3 single phase transformers. how will we generate 6 supply from 3 phase supply input