I HAVE GOT TYPICAL PROBLEM WITH THE TEMP.INDICATION.
THE PROBLEM IS THE K-TYPE T/COUPLE OUT PUT IS CONNECTED TO
A INDICATOR.THE INDICATION FLUCTUATES SOME TIMES AND SOME
TIME IT IS STABLE.
WHEN I CHECKED OUT PUT OF T/COUPLE THE MV WILL NOT VARY.
WHERE AS INDICATION FLUCTUATES.
WHEN I GIVE MV SOURCE TO T/COUPLE EXTENSIONCABLE FROM THE
FIELD IT INDICATION IS STABLE.
WHEN GIVE MV SORCE TO INDICATOR ITS INDICATION IS STABLE.
PLEASE CLARIFY.
Answers were Sorted based on User's Feedback
I agree with Mr. Satyendra Bhai Patel suggestions.
More over please check followings:
1. May be some electric motor starts and its cable routing
is near to your extension cable.
2. Also get check thermocouple,some time,its hot juction
got open and close with the passage of time. Replace
thermocouple.
3. Check loose connections.
4. Check thermocouple any wire being grounded at some time.
5. Any how, do not megger thermocouple extension wire.
Check it with normal multimeter.
aftabmazari@yahoo.com
Is This Answer Correct ? | 6 Yes | 0 No |
Answer / satyendra bhai patel
check cable is screened or not ? i think this type of
problem occures when a little bit induction in wire .so
just screen your cable in indicator s terminal.problem will
be solved .
For more details u can contact me on 9005091827
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / rana mujahid
I agree with all above answers but I think the most chances
are may be TC hot junction is some time going to open and
close..........need to replace TC
Is This Answer Correct ? | 1 Yes | 1 No |
Answer / abhishek
please check instrument cables are earthen or not with
screened cables.this things only happens when wires are cut
at gland side or terminations are loosed
Is This Answer Correct ? | 0 Yes | 1 No |
What is the principle of capacitance type level transmitter?
Why some transmitter shows flow in MMWC and some in TPH?
How many types of Control Modes in process control, plz tell me all.....?
what is start up vent valve ? why it is used in boiler?
8 Answers ACC, Bhushan Power Steel,
(1) In turbine, what does term CDP, NI, NH, HSSOC, means. (2) What is the purpose of LO overhead tank in turbines.(3) An equipment is certified for EEX, IA, IIC,T6, what do you under stand by this.(4) what is SURGE, and how it is prevented, what is the purpose of bypass valve across AS valve.(5) Give 2 application of quartz crystal used for process parameter measurement.(6) what is meant by cold float of compressor shaft. (7) state four different types of flow measurement. For gas flow measurement mmscfd is the common unit. Expand the unit and specify significance of word S in the unit.(8) what is meant by Gap voltage, in vibration measurement. Normally how much Gap voltage is set and state the reason.(9) what will the new flow factor if D/P transmitter is Re-Ranged from 25” wc to 50” wc.(10) what is the usage of QDV & Volume booster.
how to calculate the temp. of RTD&Thermocouple when we got some mV r Ohms?if anybody has d chart pls mail the chatrs to me...
2. What is ultrasonic flowmeter?
How to derive IO Count (AI, AO, DI and DO ) from a Field instrument (FI) Bill of Quantities (BOQ) given by client.
what is the procedure to callibrate temp controller ,pressure controller,etc. suppose a temp controller showing error 1.5 degree centigrate how can i minimize it.
0 Answers Sabic, Saudi Aramco Shell Refinery Company SASREF,
What is derating factor in Motor?
What is the exact output of eddy current proximity probe? For vibration mesurment?
in split range control valve,two valve should be in two different line and that should have some distance,and we have only one positioner feed back link.so how we connect one feed back in two control valves?if you have picture please forward me.my email id kb.syamkumar@gmail.com