I HAVE GOT TYPICAL PROBLEM WITH THE TEMP.INDICATION.
THE PROBLEM IS THE K-TYPE T/COUPLE OUT PUT IS CONNECTED TO
A INDICATOR.THE INDICATION FLUCTUATES SOME TIMES AND SOME
TIME IT IS STABLE.
WHEN I CHECKED OUT PUT OF T/COUPLE THE MV WILL NOT VARY.
WHERE AS INDICATION FLUCTUATES.
WHEN I GIVE MV SOURCE TO T/COUPLE EXTENSIONCABLE FROM THE
FIELD IT INDICATION IS STABLE.
WHEN GIVE MV SORCE TO INDICATOR ITS INDICATION IS STABLE.
PLEASE CLARIFY.
Answers were Sorted based on User's Feedback
I agree with Mr. Satyendra Bhai Patel suggestions.
More over please check followings:
1. May be some electric motor starts and its cable routing
is near to your extension cable.
2. Also get check thermocouple,some time,its hot juction
got open and close with the passage of time. Replace
thermocouple.
3. Check loose connections.
4. Check thermocouple any wire being grounded at some time.
5. Any how, do not megger thermocouple extension wire.
Check it with normal multimeter.
aftabmazari@yahoo.com
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / satyendra bhai patel
check cable is screened or not ? i think this type of
problem occures when a little bit induction in wire .so
just screen your cable in indicator s terminal.problem will
be solved .
For more details u can contact me on 9005091827
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / rana mujahid
I agree with all above answers but I think the most chances
are may be TC hot junction is some time going to open and
close..........need to replace TC
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / abhishek
please check instrument cables are earthen or not with
screened cables.this things only happens when wires are cut
at gland side or terminations are loosed
| Is This Answer Correct ? | 0 Yes | 1 No |
How we are deciding while programming in pid controller , What we are using heating or cooling.
Can we use twisted pair cable instead of ethernet for communication?
why we use npn sensor in vibration monitoring system
What is DCS?
How to calibrate Toxic gas detector?
how we are selecting instuments by differentiating certain instruments in 4 to 20 ma range and certain in 1 to 5 v dc
Manipulation of dead wt. tester double piston type.
in valve is constructed as per SME B 16.34, then which standard is used for fire testing of valve?.
how to convert bar to mA?
What is compensation for flow ? Why we use compensation ? What are the factors of different compensation ? We not use then what problems may happen ?
tion 0,50,100% equql to voltage formula?
In separator VFD frequently trip with OVER VOLTAGE Fault What is the reason?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)