I HAVE GOT TYPICAL PROBLEM WITH THE TEMP.INDICATION.
THE PROBLEM IS THE K-TYPE T/COUPLE OUT PUT IS CONNECTED TO
A INDICATOR.THE INDICATION FLUCTUATES SOME TIMES AND SOME
TIME IT IS STABLE.
WHEN I CHECKED OUT PUT OF T/COUPLE THE MV WILL NOT VARY.
WHERE AS INDICATION FLUCTUATES.
WHEN I GIVE MV SOURCE TO T/COUPLE EXTENSIONCABLE FROM THE
FIELD IT INDICATION IS STABLE.
WHEN GIVE MV SORCE TO INDICATOR ITS INDICATION IS STABLE.
PLEASE CLARIFY.
Answers were Sorted based on User's Feedback
I agree with Mr. Satyendra Bhai Patel suggestions.
More over please check followings:
1. May be some electric motor starts and its cable routing
is near to your extension cable.
2. Also get check thermocouple,some time,its hot juction
got open and close with the passage of time. Replace
thermocouple.
3. Check loose connections.
4. Check thermocouple any wire being grounded at some time.
5. Any how, do not megger thermocouple extension wire.
Check it with normal multimeter.
aftabmazari@yahoo.com
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / satyendra bhai patel
check cable is screened or not ? i think this type of
problem occures when a little bit induction in wire .so
just screen your cable in indicator s terminal.problem will
be solved .
For more details u can contact me on 9005091827
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / rana mujahid
I agree with all above answers but I think the most chances
are may be TC hot junction is some time going to open and
close..........need to replace TC
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / abhishek
please check instrument cables are earthen or not with
screened cables.this things only happens when wires are cut
at gland side or terminations are loosed
| Is This Answer Correct ? | 0 Yes | 1 No |
How to find the range of DP cell Transmitter for measurement of level in closed vessel.
what is different betwen Process zero and atm zero?
what is fire and gas system?
2 Answers Andhra Petrochemicals Limited,
any questions on motor and energy conversions machines?
Explain the difference between differial pressure & delta pressure?
In control valves (like feed water control valve) we will give 3 kg pressure and how it controls 110 kg of water pressure?
What is input and output of vaiberation transmitter and what is its unit.
which type of rtd is good for any system,2wire,3wire or 4 wire
what is diffrance between FF & SMART, explain with difination
0 Answers Bapco Bahrain Petroleum Company,
explane hart protocol? what is its advantages.
in my company organisation in plan to take new PLC system for replacing old relay system , for that what I/P needsd to submit to the system house of PLC supplier?
How to calibrate Toxic gas detector?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)