I HAVE GOT TYPICAL PROBLEM WITH THE TEMP.INDICATION.
THE PROBLEM IS THE K-TYPE T/COUPLE OUT PUT IS CONNECTED TO
A INDICATOR.THE INDICATION FLUCTUATES SOME TIMES AND SOME
TIME IT IS STABLE.
WHEN I CHECKED OUT PUT OF T/COUPLE THE MV WILL NOT VARY.
WHERE AS INDICATION FLUCTUATES.
WHEN I GIVE MV SOURCE TO T/COUPLE EXTENSIONCABLE FROM THE
FIELD IT INDICATION IS STABLE.
WHEN GIVE MV SORCE TO INDICATOR ITS INDICATION IS STABLE.
PLEASE CLARIFY.
Answer Posted / aftab ahmed mazari
I agree with Mr. Satyendra Bhai Patel suggestions.
More over please check followings:
1. May be some electric motor starts and its cable routing
is near to your extension cable.
2. Also get check thermocouple,some time,its hot juction
got open and close with the passage of time. Replace
thermocouple.
3. Check loose connections.
4. Check thermocouple any wire being grounded at some time.
5. Any how, do not megger thermocouple extension wire.
Check it with normal multimeter.
aftabmazari@yahoo.com
| Is This Answer Correct ? | 6 Yes | 0 No |
Post New Answer View All Answers
in valve is constructed as per SME B 16.34, then which standard is used for fire testing of valve?.
Specific gravity.
what do u mean by compensation n pid tunning?in pid tunning what you tunned?is it possible 2 tune p i d
Explain operation of Haskel pump.
3. Differentiate between ultrasonic flowmeter and radar type flow meter.
it is possible to check the fail safe condition in pressure transmitter. if possible how?
Q-Explain the different load conditions that will produced different offset which may or may not be acceptable to thhe control function
What are different type of instrument cable
we want to control pump in let pressure and tank (for exp) our inlet line if water cam and pump will on and when our tank will full pump will off also if our inlet pressure low pump will off even tank not full.this pump i want to uses on our water supply line.
what is piezoelectric transducer?give an example in power plant n state its principle?
what is the process to make control schematic ?
the whole paper was based on Transducers..questions like define repeatability, error,accuracy,precision..den there were many q. on the conversion of Pa to mmHg and other units.. also..der wer few Q. on some level sensors(with diagram)
How to calibrate H2s Dectector
How to calibration a control valve?
What is three element drum level control system why its better than single element?