What is the difference between sensitive earth fault and
restricted earth fault in power transformers?
Answers were Sorted based on User's Feedback
Answer / raghavendran
Sensitive Earth fault protection: Normally used on systems
where the earth fault current is limited to a very low
value. Scheme consists out of a ring CT (Core Balance CT)
around the three phase conductors, and the relay connected
to the secondary side of the CT. A very low setting is
possible, even sometimes lower then 1% FLA. Need to
coordinate with similar relays downstream. This method is
based on primary current vector addition or flux summation.
The conductor
cables pass through the center hole of the core balance CT.
Secondary current is the system zero-sequence current
3I_0.This scheme provides increased sensitivity with no
false residual currents. However,
care must be taken to prevent false tripping from unbalanced
inrush currents that may
saturate the current transformer core.
residual Earth Fault Relay:Restricted Earth Fault Protection
Is a type of zone of protection, or a differential scheme.
You get two types, low impedance and high impedance. Low
impedance is normally current operated and high impedance
voltage operated. High impedance REF is the most commonly
used. Relay connected in parallel with three phase CTs and
one neutral CT. It will look just for faults inside the
transformer, and need not to coordinate with relays
downstream (can operate very fast). With this kind of
protection you can protect over 90% transformer windings.
Need to use special class CTs, previously called class X
CTs.low impedance REF, are incorporated into some the new
microprocessor relays.
| Is This Answer Correct ? | 42 Yes | 5 No |
Answer / raghavendran
A Restricted Earth Fault (R.E.F.) has nothing to do with the
magnitude of the current. It is in fact a normal earth fault
that is restricted to a 'zone'. That is, the R.E.F.
protection is only looking for earth faults occuring in a
given zone. Any earth fault outside the zone (restricted
area) is ignored by the R.E.F. protection. It is typically
used on power transformers, with the protected zone
typically being between the star-point current transformer
and the phase transformers of the star-wound winding.
| Is This Answer Correct ? | 23 Yes | 6 No |
Answer / surendar
Restricted earth fault function only protect the specified
zone .But sensitive earth fault function can protect all
earth faults(only applicaple for after start of ct point).
both protection analog inputs taking from neutral ct of
power transformer.but in ref taking ct reference for all
phases of ct for making protection of specified area .
setting of ref lesser then sef.sef also back up for ref.
both protection only applicable for star side for
transformer
| Is This Answer Correct ? | 11 Yes | 6 No |
What is the BS(British Standard)code for 11kv motor
if three phase supply is given to single phase transformer, what will happen?
What is the Ohms low calculation
What is the difference between a 3 winding and 2 winding Potential Transformer
what is the difference between LATCH and FLIP FLOP
why impedance relay is used for medium transmission line protection
How the flights will be fly be fly without ground connection under raining with thunder lighting?
How does cost of generation from hydropower plant compare with other sources of electricity?
What are the advantages of skewing of cage rotor conductors?
EXPLAIN WORKING PRINCIPLE OF ALTERNATOR & MOTORS.
How to set the star delta timer setting?
what is the Excaste meaning of CT Saturation?? 10 P 20, 15 VA, what is the meaning of 10, & 20. if the CT polarrity changed what will happened?? what is the differece between measuring CT & Protection CT?? what is the Saturation Point of measuring CT & Protection CT??
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)