What is the formula to find out cross sectional area of
cable for certain current rating?
Answer / tarun aggarwal ymca
what u have to first take into mind what type of cable u want to purchase....then its size matter
usually we use XLPE insulated cable for Power cable and Aluminum or copper its depend upon the cost and loses
mean if u need large length cable you have to prefer aluminum in shorter length copper cable is preferred as its resistivity is less
for example
VLL = 11kV (line volatge)
L = 1.3km
Maximum allowable Vdrop = 2.5% of VLL i.e.Vdrop = 275V
SkVA = 3000kVA (Total Power we have to transfer of to be used by the connected load)
Full load Current If= SkVA/root3 VLL i.e If = 157.5A
Demand factor is what we actually demand the current (it not always full load current what we demand) Let D.F = 80% of If
Id =D.F x If (Demand Current) where D.F = Demand Factor i.e Id = 126.0A
The cable current carrying capacity is always kept larger than the demand current let S.F for Cable in % = 30% Extra Id
Ic= (1+S.F/100) Id i.e Ic = 163.8A
This current is what will be safer current that will be carried out by cable
Now derating factor K is calculated by the following equation
K = Kground x Ktherm.res x Kdepth x Kgroup
Vdrop = 3IdL root(Rac cos􀄳+ Xsin􀄳)
Now cable data is refered
Type 3 Core, Copper Conductor, XLPE insulated, Copper tape Screened, PVC bedded, Steel Wire Armoured, PVC, 8750/15000V.
Parameter -------- 50 mm2---- 70 mm2 ------ 95 mm2------- 120 mm2 ------- 150 mm2 ----- 185 mm2
Irated (A) --------- 187----------- 227- ------------ 267--------------303 -----------------338------------------ 383
Kground----------------0.86
Ktherm.res-- ----------- 1
Kdepth-------------------0.98
Kgroup ------------------0.7
K-------------------------- 0.590
Icor (A) -----------110.32 --------- 133.92----------157.52--------- 178.76-------------199.41------------225…
Rac (ohm/km) --- 0.493 --------0.342------------ 0.247------------0.196---------------0.1… ------------ 0.128
X (ohm/km) --------0.118 --------0.112 ------------0.106------------0.102------…
P.F = Cos--------0.85
(In radian)-------- 0.5548------ 0.5548----------0.5548-----------0.5548-…
Vdrop (V)-----------196.76-------167.73-------…
Considering the values of Ic, Icorrected and Vdrop the best suited cable is 120 mm2
cable for connecting switchyard to substation
Sorry extra long answer but i want to explain in detail
| Is This Answer Correct ? | 7 Yes | 2 No |
What is delta stare switch?
what are the available sizes of pin type terminal lugs in the market today?
how much distance is required for earth pit to earth pit in substation???
What is the working principle of MIG welding? and its out put Voltage?
What is the technical reason for adopting color coding of three phase system as RYB.
what is the name of the oil is used in transformer?
why total tape position are odd in number in Power transformer ?
how to calculate load if i have three phase & single phase connection from power transformer( in term of kw & kva).can i take single phase load/3 for total kw calculation
what will happen if instead of neutral we use earth wire as return conductor?if we can use ,then why we are not using in our day to day appliances?please justify the answer
An electric bulb giving light but at the time of lighting which one it takes? voltage or current
how to use single phase supply for a three phase equipement.
What is the necessary and sufficient condition for stability.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)