What is the formula to find out cross sectional area of
cable for certain current rating?
Answer / tarun aggarwal ymca
what u have to first take into mind what type of cable u want to purchase....then its size matter
usually we use XLPE insulated cable for Power cable and Aluminum or copper its depend upon the cost and loses
mean if u need large length cable you have to prefer aluminum in shorter length copper cable is preferred as its resistivity is less
for example
VLL = 11kV (line volatge)
L = 1.3km
Maximum allowable Vdrop = 2.5% of VLL i.e.Vdrop = 275V
SkVA = 3000kVA (Total Power we have to transfer of to be used by the connected load)
Full load Current If= SkVA/root3 VLL i.e If = 157.5A
Demand factor is what we actually demand the current (it not always full load current what we demand) Let D.F = 80% of If
Id =D.F x If (Demand Current) where D.F = Demand Factor i.e Id = 126.0A
The cable current carrying capacity is always kept larger than the demand current let S.F for Cable in % = 30% Extra Id
Ic= (1+S.F/100) Id i.e Ic = 163.8A
This current is what will be safer current that will be carried out by cable
Now derating factor K is calculated by the following equation
K = Kground x Ktherm.res x Kdepth x Kgroup
Vdrop = 3IdL root(Rac cos􀄳+ Xsin􀄳)
Now cable data is refered
Type 3 Core, Copper Conductor, XLPE insulated, Copper tape Screened, PVC bedded, Steel Wire Armoured, PVC, 8750/15000V.
Parameter -------- 50 mm2---- 70 mm2 ------ 95 mm2------- 120 mm2 ------- 150 mm2 ----- 185 mm2
Irated (A) --------- 187----------- 227- ------------ 267--------------303 -----------------338------------------ 383
Kground----------------0.86
Ktherm.res-- ----------- 1
Kdepth-------------------0.98
Kgroup ------------------0.7
K-------------------------- 0.590
Icor (A) -----------110.32 --------- 133.92----------157.52--------- 178.76-------------199.41------------225…
Rac (ohm/km) --- 0.493 --------0.342------------ 0.247------------0.196---------------0.1… ------------ 0.128
X (ohm/km) --------0.118 --------0.112 ------------0.106------------0.102------…
P.F = Cos--------0.85
(In radian)-------- 0.5548------ 0.5548----------0.5548-----------0.5548-…
Vdrop (V)-----------196.76-------167.73-------…
Considering the values of Ic, Icorrected and Vdrop the best suited cable is 120 mm2
cable for connecting switchyard to substation
Sorry extra long answer but i want to explain in detail
Is This Answer Correct ? | 7 Yes | 2 No |
How to select power cable for machine
Whatis the current capacity of 33KV/ 0.433KV transformer on Primary and secondary side/
Even when a particular generator in a generating station is under maintenance we are still able to maintain the same power output. How is this possible? Does the tie line between 2 generating stations have a role to play in it?
Why the high starting current does not harm the low capacity induction motor?
Why we are mostly using a single 3-phase transformer instead of three 1-phase transformers?
How can claculate to attain the desired PF in the line ( HOW Much KVAR is required ) Pls Give the formula? Equate Petrochemical 0 1 how to calculate sizing of NGTR (Transformer rating,Loading resistor value and Current rating of resistor) and what is the X/R ratio. Details : 11kV,Capacitance 1.73532 micro farads,40kA for 1sec. 0 1 What will happened. if we feed 3phase supplay to the stater with out insert the rotor. How much current will flow through the stater winnding? Equate Petrochemical 0 1 What is required of exietation to the alternater. 0 1 why star point of HT motor not earthed? Equate Petrochemical 0 1 Why we are getting low voltage in star connection? Equate Petrochemical 0 2 What's ND relay & it's functions? Equate Petrochemical 0 2 How instantanious short circuit current is calculated? its formula? Equate Petrochemical 0 2 What is servo Motor? What's the advantages of this motor over Induction motor? Equate Petrochemical 0 2 What is core CT & it's function? Equate Petrochemical 0 3 what is meant by star/delta voltages as 440/220 in a 3 phase induction motor, and why it should be connected on STAR IN 3 PHASE SUPPLY L & T 0 4 What is required of exietation to the alternater. KNB 1 23 what is the design voltage for 6.6KV 2000 KVAR HT capacitor? Consultancy 0 3 Pls explain about vfd control?Where it is used, Give some example? siemens 1 22 Please explain me abt PQ diagaram in the power sector. 0 9
DG Earth Value?
0 Answers Reckitt Benckiser, Vodafone,
Mention the disadvantages of low power factor? How can it be improved?
IN electrical field, WHAT ALL THINGS THE CUSTOMER WILL ASK WHILE ORDERING FOR LT PANEL (ALL TYPES OF LOW TENSION PANEL)
I want formula to calculate cable size as per load given in length & amp. I searched many sites but didn't right answer. Please reply me asap.
One B.O.T Unit ??
I have an existing old MCCB. ABB Model SACE, the rating are: Ue = 660 volts, Iu =1250 Amps, 3 poles, Ith (max) =800 amps at 45 deg C. I need a circuit breaker for my 3 phase motors, 380 volts 60 hz. the supplier required the minimum ampacity of the breaker to be 911 amps. can i use this breaker with rating of Iu =1250 amps but Ith = 800amps maximum?