Answer / 3nath
for efficient operation we have to maintain unity power factor(1) but it is possible only for resistive loads
that's why in EB lines trys to maintain approximately 1 that is 0.99 to decrease the losses. capacitor bank used to POWER FACTOR correction
| Is This Answer Correct ? | 10 Yes | 2 No |
Generally capacitors are used to improve power factors in inductive loads... Inductive load will reduce the current phase with voltage.. so lagging power factor is obtained.. in order to recover that, capacitance is provided which will reduce the voltage phase with current..so the pf remains almost near to 1(not exactly one)...
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / perambalur sakthivel
(1)the cosine angle between voltage and current is called
power factor ,
already we know very well about cos value
cas 0= 1
(2)whenever the cosine angle between voltage and current
zero time a full power is utilized / consumed
but power factor lagging time a full power is not
utilized/consumed
(3)so we are maintained in power factor in unity
(4) to regulate voltage in power system we are used in
capacitor bank used(vanthni@yahoo.com)
| Is This Answer Correct ? | 2 Yes | 1 No |
If UG power cable both ends are to be earthed or what? If not why?
which braking is used in traction motor and what is its working send at mukeskumar27@hotmail.com
if only one generator is running in droop mode parrallel with grid and suddenly grid breaker off what will happen? It will trip o/u freq or stay as it is? (urgent)
Why usually in all electrical equipment taking more current in Y pahse like pumps,compressor,or any other applications
What facility we get after CT secondary earthing and how?
what is the use of tertiary winding?
I have running 4 generator in paralel.All generators Voltages is same(470 V),KW also same (100 KW) but only No2 generator Amper is high than another generators. DG No:1,3,4 470V,100KW, 150 A DG No:2 470V,100KW,400 A
wat is the difference between real power and reactive power..which is useful..?and how it s useful..wat is the effect of these on a power system...
How to decide the fuse ratings for potential transformer
Question about ct secondaries connections?
why we test the core balance of the transformer?
how does the rotating m.m.f is produced in the 3-phase induction motor and how the poles are created in 3-phase induction motor ?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)