what are protective device needed to power a
360W ,50hz,240v,single phase,0.65 pf universal motor
Answer / suresh natarajan
Active Power: 360 Watts
Apparent Power:360/0.65=554 VA
Load Current 554/240=2.31 Amps
Protection Device should be 3-5 Amps.
| Is This Answer Correct ? | 14 Yes | 1 No |
DRAW THE DIFFERENCE BETWEEN GROUND AND NEUTRAL IN BOTH SINGLE PHASE AND THREE PHASE?
ups battery design formula
what is mean by lookup table in microprosser.
what the principle of sincroscope?how it works?when it needed?
can a generator with 15AH specified battery for starting can be connected to a battery of greater capacity?
How to calculate phase to phase difference in 33KV Line ,11KV Line etc.
What are the protection used for alternator,transformers.
what is rated current and operating current?
why the field winding of synchronous machine is excited by dc source
what is static excitation and dynamic excitation of synchronous generator,scr excitation is a brush or brushless excitation?
which fault current is maximum: 3 phase short circuit, LG, LL or LLG?? why?? in one of the problems that i have solved, 3 phase short circuit current on an unloaded generator came out to be less than the LG fault current. can anybody please explain why.
How the power factor is more in high speed machines
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)