what are protective device needed to power a
360W ,50hz,240v,single phase,0.65 pf universal motor
Answer / suresh natarajan
Active Power: 360 Watts
Apparent Power:360/0.65=554 VA
Load Current 554/240=2.31 Amps
Protection Device should be 3-5 Amps.
Is This Answer Correct ? | 14 Yes | 1 No |
what is the significance of tan&delta and how it performed in power transformer
Electrical 'C' license full abbreviation , and full form
in our 6.6kv motor feeder[it is having two sources from Bus A&B] earth fault relay is acting, we checked CBCT connection and cable meggerd values found very good still earth fault acting during first two are three start after that it will hold. please clarify what was the reason. if same motor is starting from other Bus-A it will start.
Difference between megger test equipment and contact resistance meter test instruments?
what is ten delta test? what is the significanse of it
how can i determine the KVA/MVA rating of transformer precisely?? is there any standard test?????
What is the scale analysis for condensor of HVAC system
1- What is the Polarization Index number be good for 15KV 3c#500MCM electrical cable? 2- Can I use the IEEE Std 43-2000 to perfom the PI test? Thanks
why contactor not provided between output of VFD and motor?
why the starting voltage drop in a cable needs to be limited?what is percentage of the voltage drop allowed during starting?
I have iti elec, 1st aid, and 5 yrs experience in 7.5 mw power plant. Am i eligeble for 11kv license in telangana state..when, how to apply for that.?
hot water tank,top element 240v across,the bottom 120v across,why?