Why transformer, generator, ups rating kva?

Answers were Sorted based on User's Feedback



Why transformer, generator, ups rating kva? ..

Answer / vishal ingle

rating is given in KVA / MVA because the power factor of
the lod to be connected is not known. for a specific fixed
real power (MW), the current depends on the power factor.
higher the p.f., lesser is the current & viceversa.
the condustor size inside the trf/ alternator is decided
depending on current.
hence KVA capacity is mentioned always.

Is This Answer Correct ?    10 Yes 2 No

Why transformer, generator, ups rating kva? ..

Answer / faraz haider

well,kva stands for kilovoltampere.generally in the transformer two types of losses occur.one is d copper loss&other is d iron loss.cu loss depends upon d current flowing in d transformer whereas iron loss depends upon d voltage in d transformer.so d kva rating generally specify d losses occuring in d tansformer.dats is why transformer, generator, ups r rated in kva.

Is This Answer Correct ?    9 Yes 8 No

Post New Answer

More Electrical Engineering Interview Questions

What is the difference between Earth and Neutral?

2 Answers  


How to run 1ph motor(230 VOLTS its full load amps is 4.5 ampa))with 480 volts main(we didn hav neutral)Thn we go for step down transformer.Our load 10 amps,so we conisder this amps in primary are secondary side?

1 Answers  


How to megger test 11 kV cable and the acceptance IR value

0 Answers   BVG, NFL, ONGC,


How servo stabilizer works.

0 Answers  


why should we have to maintain pf in our site 0.9????????

3 Answers   Dalkia,






Does power factor vary with speed?If yes, how?If not, why?

4 Answers   Genco,


Can anybody tell abt concrete encased earthing or grounding?

0 Answers  


How much depth n width required for laying of 1X70 Sqmm Cable in Desert???

0 Answers   Alka Electromech, Aramco,


what is the difference betweem star connected motor & delta connected motor?

0 Answers  


what happen if the supply is given to the stator of the 3phase induction motor with out assembling the rotor ?

0 Answers  


Two alternators say 1 & 2 are poised to parallel operation. But at the time of paralleing alternator 2 gets out of the system by tripping Earth fault relay. Please send me reply why this is happening?

2 Answers  


Why we are use dol starter up to 10 hp

0 Answers  






Categories
  • Civil Engineering Interview Questions Civil Engineering (5075)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4444)
  • Electrical Engineering Interview Questions Electrical Engineering (16597)
  • Electronics Communications Interview Questions Electronics Communications (3915)
  • Chemical Engineering Interview Questions Chemical Engineering (1092)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (214)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (258)
  • Instrumentation Interview Questions Instrumentation (2987)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (123)
  • Power Plant Engineering Interview Questions Power Plant Engineering (170)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (0)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1377)