hello dear
i have faced problem in drum level transmitter.
the problem is when i engrize the meter meter shows 100%
but the actual level 40 or something plz suggest me
Answers were Sorted based on User's Feedback
It seems that transmitter low side leg is leaking, or low
side is not being fully condensing.
Please chck low leg fittings, connections and if ok. Then
check transmitter high side and low side pressures with the
help of digital pressure gauge. May be transmitter low side
any problem.When you calibrate tranmitter workshop, also
apply pressure to its low side, indication should go down
to confirm that low side is ok.
aftabmazari@yahoo.com
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / s.arunraja
Please give me the Transmitter Calibration Range
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / yomama
The impulse tubes must be filled with process fluid or fill
fluid such as glycol. Additionally the specific gravity of
the fill fluid must be calculated in reference to the
process fluid being measured
Glycerin (Specific Gravity=1.26) for the impulse tubes a
correction must be made.
DP span of 100”= physical height difference of impulse tubes
on vessel
SG of fluid being measured (Oil = 0.68)
Glycerin filled tubes (SG = 1.26)
Since the Low Pressure Leg will be filled with Glycerin we
multiply the span by the SG of the Fill Fluid
100” x 1.26 = 126” so the Lower Range value will be -126”
Span will be the LRV – (SG of fluid) x ( tank Level span) = 68”
-126” + 68” = -58”
-126 LRV
-58 URV
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / yomama
The impulse tubes must be filled with process fluid or fill
fluid such as glycol. Additionally the specific gravity of
the fill fluid must be calculated in reference to the
process fluid being measured
Glycerin (Specific Gravity=1.26) for the impulse tubes a
correction must be made.
DP span of 100”= physical height difference of impulse tubes
on vessel
SG of fluid being measured (Oil = 0.68)
Glycerin filled tubes (SG = 1.26)
Since the Low Pressure Leg will be filled with Glycerin we
multiply the span by the SG of the Fill Fluid
100” x 1.26 = 126” so the Lower Range value will be -126”
Span will be the LRV – (SG of fluid) x ( tank Level span) = 68”
-126” + 68” = -58”
-126 LRV
-58 URV
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / anwer
an instrument calibration range should be 60-80% and another
condition is range shall be more than max value.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / kakhlaq
re-check the transmitter range, process connections, if
this arrangement is wet leg type then check that the leg is
filled with liquid.
| Is This Answer Correct ? | 0 Yes | 2 No |
how many types 0f thermocouples?
plz send me general of ongc
What is the difference between instrument earthing and normal earthing? and why is it necessary to do so?
what is the input of digital counter during the the calibration time?
What is meant by cold float of compressor shaft.
plz... clarify my answer, how to calibrate vaccum (DP)leveltransmitter,it is hart. (digital).DETAILS:(coloumn)closedtank height 2650mm,and tx range is 0-1500mmH20.
how to callibrate a new i/p converter
how to calibrate absolute pressure transmitter
What is PDS and PDMS ?
Introduce yourself which is not present in your biodata?
wt kind of business we can do by usig PLC?
compare the thermocouple and pyrometer,which one is the best?why?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)