Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


hello dear
i have faced problem in drum level transmitter.
the problem is when i engrize the meter meter shows 100%
but the actual level 40 or something plz suggest me

Answers were Sorted based on User's Feedback



hello dear i have faced problem in drum level transmitter. the problem is when i engrize the mete..

Answer / aftab ahmed mazari

It seems that transmitter low side leg is leaking, or low
side is not being fully condensing.
Please chck low leg fittings, connections and if ok. Then
check transmitter high side and low side pressures with the
help of digital pressure gauge. May be transmitter low side
any problem.When you calibrate tranmitter workshop, also
apply pressure to its low side, indication should go down
to confirm that low side is ok.

aftabmazari@yahoo.com

Is This Answer Correct ?    1 Yes 0 No

hello dear i have faced problem in drum level transmitter. the problem is when i engrize the mete..

Answer / ikraamh5

plz give me answer

Is This Answer Correct ?    2 Yes 2 No

hello dear i have faced problem in drum level transmitter. the problem is when i engrize the mete..

Answer / s.arunraja

Please give me the Transmitter Calibration Range

Is This Answer Correct ?    0 Yes 0 No

hello dear i have faced problem in drum level transmitter. the problem is when i engrize the mete..

Answer / yomama

The impulse tubes must be filled with process fluid or fill
fluid such as glycol. Additionally the specific gravity of
the fill fluid must be calculated in reference to the
process fluid being measured

Glycerin (Specific Gravity=1.26) for the impulse tubes a
correction must be made.

DP span of 100”= physical height difference of impulse tubes
on vessel

SG of fluid being measured (Oil = 0.68)

Glycerin filled tubes (SG = 1.26)

Since the Low Pressure Leg will be filled with Glycerin we
multiply the span by the SG of the Fill Fluid

100” x 1.26 = 126” so the Lower Range value will be -126”
Span will be the LRV – (SG of fluid) x ( tank Level span) = 68”

-126” + 68” = -58”
-126 LRV
-58 URV

Is This Answer Correct ?    0 Yes 0 No

hello dear i have faced problem in drum level transmitter. the problem is when i engrize the mete..

Answer / yomama

The impulse tubes must be filled with process fluid or fill
fluid such as glycol. Additionally the specific gravity of
the fill fluid must be calculated in reference to the
process fluid being measured

Glycerin (Specific Gravity=1.26) for the impulse tubes a
correction must be made.

DP span of 100”= physical height difference of impulse tubes
on vessel

SG of fluid being measured (Oil = 0.68)

Glycerin filled tubes (SG = 1.26)

Since the Low Pressure Leg will be filled with Glycerin we
multiply the span by the SG of the Fill Fluid

100” x 1.26 = 126” so the Lower Range value will be -126”
Span will be the LRV – (SG of fluid) x ( tank Level span) = 68”

-126” + 68” = -58”
-126 LRV
-58 URV

Is This Answer Correct ?    0 Yes 0 No

hello dear i have faced problem in drum level transmitter. the problem is when i engrize the mete..

Answer / anwer

an instrument calibration range should be 60-80% and another
condition is range shall be more than max value.

Is This Answer Correct ?    0 Yes 0 No

hello dear i have faced problem in drum level transmitter. the problem is when i engrize the mete..

Answer / kakhlaq

re-check the transmitter range, process connections, if
this arrangement is wet leg type then check that the leg is
filled with liquid.

Is This Answer Correct ?    0 Yes 2 No

Post New Answer

More Instrumentation Interview Questions

why we take %i0.0 as input for twido plc

0 Answers  


HI THIS IS NOOR AHMMAD.SHAIK, I AM WORKING IN INSTRUMENTATION MAINTENANCE Dept. in BOILER HOSE(BHEL HYDERABAD),,any other persons are working in same dept. i want some HELP in my subject

1 Answers  


What is difference between radial vibration and axial vibration explain in detail .

0 Answers   Emerson,


1. Pl. send details about different types Gas Analyser, like Co2, O2, SOX/NOX, etc. with calibration procedure. 2. How to calibrate H2S gas detector in field?

1 Answers   HPCL, Napesco,


In separator VFD frequently trip with OVER VOLTAGE Fault What is the reason?

4 Answers  


Hi, I am Newely Joined in Construction company instrument engineer? Any one can Plz tell me How can I advanced preparation for Releated Engineering and construction Documents?

0 Answers  


Q1]IF THE RANGE FOR FLOW IS -35 TO 125 WHAT WILL BE THE SPAN FOR ABSOLUTE AND FOR NORMAL? Q2]HOW TO CALIBRATE CAPILLARY TYPE LT? Q3]HOW MANY ERROR CALCULATIONS ARE THERE USED IN PROCESS INDUSTRIES? Q4]HOW TO CALIBRATE TEMPERATURE TRANSMITTER? Q5] HOW TO CALIBRATE LEVEL TROLL AND HOW TO CONNECT? Q6]PLEASE TELL ME THE BASIC FOR INSTRUMENTATION WHICH IS APPLIED FOR CALIBRATION AND FOR ALL? PLEASE MAIL THE ANSWER TO honest_yes@yahoo.in

0 Answers   Cegelec, Honeywell,


What is output of Thermocouple at 25 deg c

10 Answers   TATA,


Wht should be the ratio of natural frequency (Fn) to wake frequency (Fw) and wht if goes above the rato limit?

2 Answers  


1 > HOW TO MEASURE INTERFACE LEVEL 2 > DIFFERENCE BETWEEN RADAR & ULTRASONIC LEVEL TRANSMITTER

3 Answers   Atul Auto,


Working principle of magnetic flow meter ......and calibration procedure of e+h magnetic flowmeter...

0 Answers  


Can anybody tell me which type of question are asked in the interview for the FORMULATION(Pharma) as a instrumentation engineer, & question in building managment system.

0 Answers   Reddy Labs, ScienceWay,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)