hello dear
i have faced problem in drum level transmitter.
the problem is when i engrize the meter meter shows 100%
but the actual level 40 or something plz suggest me
Answers were Sorted based on User's Feedback
It seems that transmitter low side leg is leaking, or low
side is not being fully condensing.
Please chck low leg fittings, connections and if ok. Then
check transmitter high side and low side pressures with the
help of digital pressure gauge. May be transmitter low side
any problem.When you calibrate tranmitter workshop, also
apply pressure to its low side, indication should go down
to confirm that low side is ok.
aftabmazari@yahoo.com
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / s.arunraja
Please give me the Transmitter Calibration Range
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / yomama
The impulse tubes must be filled with process fluid or fill
fluid such as glycol. Additionally the specific gravity of
the fill fluid must be calculated in reference to the
process fluid being measured
Glycerin (Specific Gravity=1.26) for the impulse tubes a
correction must be made.
DP span of 100”= physical height difference of impulse tubes
on vessel
SG of fluid being measured (Oil = 0.68)
Glycerin filled tubes (SG = 1.26)
Since the Low Pressure Leg will be filled with Glycerin we
multiply the span by the SG of the Fill Fluid
100” x 1.26 = 126” so the Lower Range value will be -126”
Span will be the LRV – (SG of fluid) x ( tank Level span) = 68”
-126” + 68” = -58”
-126 LRV
-58 URV
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / yomama
The impulse tubes must be filled with process fluid or fill
fluid such as glycol. Additionally the specific gravity of
the fill fluid must be calculated in reference to the
process fluid being measured
Glycerin (Specific Gravity=1.26) for the impulse tubes a
correction must be made.
DP span of 100”= physical height difference of impulse tubes
on vessel
SG of fluid being measured (Oil = 0.68)
Glycerin filled tubes (SG = 1.26)
Since the Low Pressure Leg will be filled with Glycerin we
multiply the span by the SG of the Fill Fluid
100” x 1.26 = 126” so the Lower Range value will be -126”
Span will be the LRV – (SG of fluid) x ( tank Level span) = 68”
-126” + 68” = -58”
-126 LRV
-58 URV
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / anwer
an instrument calibration range should be 60-80% and another
condition is range shall be more than max value.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / kakhlaq
re-check the transmitter range, process connections, if
this arrangement is wet leg type then check that the leg is
filled with liquid.
| Is This Answer Correct ? | 0 Yes | 2 No |
Hello-I know this not an engineering question,I am working in gulf & i want to do correspondence diploma in instrumentation,can any one give me the address of any university in which this courses are available.
What is the difference between instrument earthing and normal earthing? and why is it necessary to do so?
IN CONTROL VALVE SPECIFICATIONS GENERALLY TERM " DE- 200" ."DM -400"USED,, WHAT IS DE/ DM STANDS FOR?
what are different types of cables used in instrumention how to calibrate a level transmitter online ( rosemount )
Calibration of flow transmitter.
What is the main difference between Cavitation and Flashing?
what is solenoid valve?
what is the principle of ultrasonic flowmwter and radar type flowmeter?
how can loop single 4-20 ma to two isolation amplifier? i mean i have two isolation amplifier with 4-20 ma input and 1-5 v output.can i done series connection ?
can you give some devices that measure directly the mass flow rate.
What is pipe schedule? What are all effects its having in the valve? how do we take care of pipe sch in case if the customer dint specify in the data sheet. What we need assume and in what basis?
WHEN BOTH WIRES OF THERMOCOUPLE R SHORTED WHAT IS THE OUTPUT THE TEMP ARE 0,30,250,320
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)