suppose in dcs range of a flow transmitter is 10t/hr what
is dp for 50% in 2500mmwc
Answers were Sorted based on User's Feedback
Answer / mithilesh kumar
tx range in dcs is 0-10 t/h.ok.
if ur TX showing 50% and 1250 mmwc then after square root
it is near 70% then in dcs ie that flow is 7 T/H.
if tx is showing 25% then this time mmwc will be 625.
after square root it is 50% and in dcs shows 5 T/H.
any comment u welcome
Is This Answer Correct ? | 9 Yes | 0 No |
your DP will be 1250 mm h2o but if you want what will be flow at 50% then simply 50 under root multiple 10,= about 70%
Is This Answer Correct ? | 5 Yes | 2 No |
Answer / david gibbs
You need to work out the square root of the 50% reading you
require as flow is not linear.
The square root can be calculated at transmitter or DCS
Is This Answer Correct ? | 3 Yes | 3 No |
What is fault tolerent system
why is an oxygen sensor used in a boiler stack
For what reason would you possibly be compelled to make use of a Smith Predictor. Explain the idea behind the operation of this device.
Derive capacitance to 4-20ma conversion formula / relation in capacitance type pressure sensor?
HI FRIENDS IHAVE QUESTION 1.WHAT IS PARTIALSTROKE TEST?WHY IT IS USED ON ESD ON OFF VALVES?
NAME ANY TWO ELASTIC PRESURE SENSOR?
What is difference between flame retardant & flame resistance cable? Among which type of cable is used for ESD & Fire and Gas system application?
Identification of ss fittings, pilot valves, relief valve.
what is difference between wheatstone bridge, pirani gauge and strain gauge ??? explain its principle and working
Boolean algebra
Difference between dcs and plc including date processing and architecture.
what is the difference between single and double compression cable gland