what do you mean by mf of energy meter & its formula?
Answers were Sorted based on User's Feedback
Answer / sagar parmar (getco)
this one is the correct formula, sorry for previous mistake
Multiplying Factor = (yard CT Ratio x yard PT ratio)/(Meter
CT Ratio x Meter PT Ratio)
| Is This Answer Correct ? | 45 Yes | 4 No |
MF means the Multiplying factor.
Its nothing but the CT ration . as a big amount of the
current to be measured So direct Metering is not possible
hence CT operated meter is used
Formula :- if the CT ratio is 60/5 then metered reading
should be multiply by 12 which give the exact Power usage
| Is This Answer Correct ? | 28 Yes | 8 No |
Answer / sagar parmar (getco)
Multiplying Factor = (yard CT Ratio x yard PT ratio)/(Meter
CT Ratio x Yard PT Ratio)
| Is This Answer Correct ? | 14 Yes | 6 No |
what can be the causes of capacitor start motor having a higher current that its actual
i need list of swg(standard wire guage) or area of conductor v/s current carrying capacity of conductor copper & alluminium...
what you mean swtchgear(electrical)
what will happen reduce the transformer voltage from 415v to 406v, is it save the energy,? are this methodis good to reduce the energy.?
if an insulated power and control cables of a running gas diesel gensets laid direct in an open trench i.e, trench bed is not rcc of a power house in which rain water, spillage water alwas exists and all power control cables remains submerged even when gas gensets of 480 kw each runningin on load. These power &control cables runs from power house to switchgear room through these trenches in which water remains most of the time. pl explain its merit & de-merit
what is ment by doublefield revolving theory?
define transient state &steady state
how does calculate loss correction factor in transformer
how to find motor contactor rating and bimetalic relay rating? of 30kw motor which will operate on star-delta starter?
Why the meters sonnected to metering core of CT are not damagedon event of a fault??? Explain the phenomena??
what is the k var ratting of 1250kva
what is the basis for selection of Protection CT class ? How anyone can decide whether to go for 5P10 or 5P20 ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)